I'm after some advice please, I have carbon mat underfloor heating throughout my bungalow, each room has its own thermostat and are fed via a fused spur , these make virtually no sound, whereas my living room is a much larger area of around 40m2 and has its own thermostat and is fed from up in the loft via contactors. These make a very loud clunking noise every time it clicks on and off, it can be heard all over the bungalow. I have attached a picture of my control box and contactor and wondered if there were some quieter contactors on the market. The contactor box is mounted on a wooden frame in the loft and sits on the joists up there, maybe I could mount it on some soundproofing ? any advice would be appreciated
 

Attachments

  • qqq.jpg
    44.2 KB · Views: 11
  • qqqq.jpg
    65.7 KB · Views: 11
In principle you could have the contactor replaced by a solid state relay of appropriate current rating.
This is an example, but need to check the current consumption of the mat(s) first:

There are options around both the current rating and the control voltage, but I'm guessing your contactor coil is mains, in which case an SSR with mains trigger might be a 'drop-in' replacement.
 
Last edited:
  • Like
Reactions: DPG

Reply to Contactor for carbon mat under floor heating in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi there I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat ...
Replies
7
Views
817
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Hi. Can anyone offer a bit of advice please. I've got a customer who wants needs an upgrade to their consumer units. It is a bungalow that has a 3...
Replies
11
Views
7K
I have absolutely zero experience with MVHR. The issue I have in my own home is as follows. Log fired burner in kitchen supplies hot water and...
Replies
8
Views
1K
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock