I have a DOL starter (https://docs.rs-online.com/c08c/0900766b81586106.pdf for reference) that I want to connect to my ac motor. I understand that the dol starter has a built-in contactor. I want to connect two other switches, a tilt and a proximity switch. Is it possible to connect these two switches to this DOL? If not how would I go about this?
This video should help, form 15;00 mark onwards

Simply put a start device can be on parallel with existing, a stop device MUST go in series.

You just need to check if these additional switcheswpuld be Normally Closed (NC) or Normally Open (NO) in operation - If they're devices to interrupt operation they will likely be NC in operation (Opening if tilt or person proximity is detected or (in the case of a deadman style proximity - closing in the presence of a person and opening (stopping) if the person walks away)

 
What voltage is the contactor coil?
What voltage are the contacts in your external detectors / controls rated for?
Is there any machine safety functionality related to these controls and if so, what do your risk assessment and IEC 60204 (amongst others) say about that?
 
Think hes looking to add it to the stop starter he shared link of.. go on that one lucien, I dont think can be done with that switch on it's own, you need more contactors planted .
 
As lucien points out here we would need a lot of info before we could advise crucially the function of the motor and the underlying reasons for fitting the stop circuit limits.

Your profile suggests you are not qualified in the electrical industry so as a forum we have to be careful that any advice given reflects such, we may indeed be able to give guidance and help here but it does come down to what you are attempting to do, why and on what.
 

Reply to Contactor to DOL starter & switches in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
317
Guys I have 2 DOL starters which share the same supply for 2 toilet extract fans I have a selector switch wired up and and a set of auxilliary...
Replies
3
Views
1K
Hi all From the outset I'm not in an electrician. I am posting here because I'm thinking the subject matter is quite specific and will prob...
Replies
43
Views
6K
I am back to try and hook up my Frankenstein compressor. 60 gal tank, Ebay 5hp motor, HF 5 HP, 145 PSI V-Style Single Stage Cast Iron Air...
Replies
0
Views
516
Looking for counsel / guidance to replace an original Dayton On/off with speed control switch. I’ve checked with a couple local electrical supply...
Replies
5
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock