Search for tools and product advice,

Discuss continuity in the UK Electrical Forum area at ElectriciansForums.net

Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.
 
Overskilled that is what Richard pointed out even doing a R2 test there is a good chance that you will get some sort of reading if there is metal work throughout the installation, by picking up parallel paths.

If you don't get a reading of any kind then I would do an IR test with the MET to confirm that there is no potential
 
Overskilled that is what Richard pointed out even doing a R2 test there is a good chance that you will get some sort of reading if there is metal work throughout the installation, by picking up parallel paths.

If you don't get a reading of any kind then I would do an IR test with the MET to confirm that there is no potential
Wasn't a reply when I hit post. Consider entry retracted
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.
Agree with this 100%
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.

Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?
 
Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?

That figure is suggested for the resistance of the connection to the part being bonded only, not the bonding cable. Ie you test between the cable terminal of the earthing clamp and the pipe it is attached to and this should have minimal resistance with 0.05 being the suggested guideline maximum
 
That figure is suggested for the resistance of the connection to the part being bonded only, not the bonding cable. Ie you test between the cable terminal of the earthing clamp and the pipe it is attached to and this should have minimal resistance with 0.05 being the suggested guideline maximum

Are you sure about that? I think the ruling is that the recommendation is that the main bonding' resistance should be 0.05 Ohms, anything greater then you should look into increasing the CSA of your main bonding conductor. The figure of 23Mohm relates to the resistance of any extraneous metal work measured from a known earth, anything less then that makes it an extraneous part and thus should be bonded.
 
Last edited:
Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?
GN3 only suggests that the resistance of a main bonding conductor should be in the order of 0.05Ω, however this is patently incorrect as I have measured bonding conductors reading 0.00Ω on my meter!
If you say that 0.00Ω is in the order of 0.05Ω then so is 0.10Ω so what is the point in them saying 0.05Ω.
In a domestic property it is likely that the resistance of a bonding conductor is <<0.05Ω because you cannot get the physical length required, in an industrial setting then it is likely that the sheer mass of parallel paths will reduce the resistance measurement to similarly <0.05Ω, in a commercial setting you may get bonding long enough to exceed 0.05Ω without parallel paths but it would still be firmly connected to the MET with a low resistance path.
When measuring the resistance of the bonding conductor you are really checking it is connected not that it has a specific resistance, if you get 0.3Ω then there is probably something wrong.
As said in other posts GN3 also says that the bonding clamp to extraneous conductive part resistance should be of the order of 0.05Ω; so which is it? the total resistance or just the joint, you cannot have both!
I am veering away from BS7671 and just putting my opinion here but it does seem sensible to me.
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.

Whats wrong with powering down and disconnecting the bonding conductors from the MET, then measuring to the gas / water pipe where accessible?
 
If you do that with an unidentified conductor that you do not know where it is connected you may be making a mistake, in all likelihood you are testing a 10mm² green and yellow cable that is probably bonding, but not with surety as I say, it may be you are testing the actual water bond cable and getting continuity to gas via the boiler and so when you test this cable you get a low resistance to the gas pipe, great gas is bonded, no it is maybe connected by the FCU cpc for the boiler?
If you can see where it starts and stops then you have more surety.
If you test another cable and get lower resistance that might be the right cable, who can be sure.
You may be able to make a reasonable assessment but is it right?
 
For main equipotential bonding, there is no single fixed value of resistance above which the conductor would be deemed unsuitable. Each measured value (if it's measurable) should be compared with the relevant value for a particular conductor length and size.
 
Surely can disconnect every cpc that could cause a parallel path to earth (boiler, shower, imm. heater etc) and then individually test each bonding cable to gas / water via long lead??
 

Reply to continuity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
768
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
458
OLDBOY
O
I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
765

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock