Discuss Cooker diversity with SEPARATE oven/hob in the UK Electrical Forum area at ElectriciansForums.net

J

Justme761

Hi all,

Looking at replacing kitchen. Current setup is 2.2kw oven, 5.6kw hob.. total = 7.8kw on 6mm cable, back to a 40a breaker. The current cable run is short..

2m from CU, in breezeblock/plaster..
2m clipped direct, to a 45a switch (for oven in tower)..
3m spurred from that, on more 6mm, to another 45a switch (for hob)..

Want to replace this with a 4.4kw double oven, same 5.6kw hob, total = 10kw.

Applying diversity, all looks good...

10,000 / 240 = 41.67 amps.. -10 = 31.67 amps * 0.3 = 9.5 amps + 10 = 19.5 amps

BUT, it's dawned on me this is a separate oven/hob combo, not a big all-in-one thing. Does this make any difference to the calculation? I'm just thinking if this was an all-in-one type, it'd have knowledge/control over what its own heating elements were doing, so would presumably ensure it didn't use more than the 10+30%, which is I guess what manufacturers quote to people putting the regs together?

Hope that makes sense - basically, is the calculation any different when it's an all-in-one oven/hob, or separate oven and hob?

Many thanks,

Shaun.
 
You should perform the calculation separately for each appliance, and also take heed of the manufacturer's installation instructions as these may stipulate minimum connection particulars above that of the calculated diversity values.

I can't see you having a problem though.
 
You should perform the calculation separately for each appliance, and also take heed of the manufacturer's installation instructions as these may stipulate minimum connection particulars above that of the calculated diversity values.

I can't see you having a problem though.
Hi Andy78,

Thanks for the input, that makes sense. Doing for each I get..

4,400 / 240 = 18.33 amps.. -10 = 8.33 amps * 0.3 = 2.5 amps + 10 = 12.5 amps
5,600 / 240 = 23.33 amps.. -10 = 13.33 amps * 0.3 = 4 amps + 10 = 14 amps
TOTAL = 26.5 amps (Difference +7 amps)

..which looks like it'll still be fine on 6mm and 40amp breaker?
 
How many cooks are going to be using this cooking equipment at any one time?
Hi Snowhead,

Just the one cook involved, but I regularly taste her kitchen output, and some can be on the ropey side. But I'm not sure if I could describe her as 0.75 of a cook? :)

Is the thinking that if it's just one person, usage won't be all heating elements at once - so all good?
 
You should perform the calculation separately for each appliance, and also take heed of the manufacturer's installation instructions as these may stipulate minimum connection particulars above that of the calculated diversity values.

I can't see you having a problem though.
PS. Have checked one of the manuals online, the one for the oven not bought yet. Skimpy little thing. Nothing mentioned at all bar the wattage and the cable that should be used (6mm) but of course that's not with the hob in the equation. Will try and find instructions for hob online as it's one we've had for a while and the original is long gone....
 
Hi Andy78,

Thanks for the input, that makes sense. Doing for each I get..

4,400 / 240 = 18.33 amps.. -10 = 8.33 amps * 0.3 = 2.5 amps + 10 = 12.5 amps
5,600 / 240 = 23.33 amps.. -10 = 13.33 amps * 0.3 = 4 amps + 10 = 14 amps
TOTAL = 26.5 amps (Difference +7 amps)

..which looks like it'll still be fine on 6mm and 40amp breaker?
Hi All,
Newbie has a question, is there a reason for sticking with 40A breaker and not dropping down to a 32A?
 

Reply to Cooker diversity with SEPARATE oven/hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
770
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
826
Hi Guys, I am just changing my plug top oven over & gas hob and noticed the following: 32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock