Discuss cooker diversity in the Australia area at ElectriciansForums.net

Applying diversity to a cooker is as follows.

Take the full load, 39.13A.

Take the first 10A of this, add 30% of the remaining current i.e 30% x 29.13 = 8.73A

Total load after diversity = 10A + 8.73A = 18.73A.

Also if the control unit has a socket outlet incorporated then you add an additional 5A.


So does that.^^^;)
 
Are you guys being serious??
Generally cooker supplies go in at either 32 or 40 amps, there is nothing out of the ordinary with the cooker being installed so dont trouble yourself over this.
Read the onsite guide, its there for a reason and you will be well within the capability of a 6 mm cable, assuming the run is not overly long
 
...but obviously didnt trust the answer.

Obviously hes not the only one. But as Sparks1234 quite rightly said, we`ve been given ample guidance to arrive at a sensible CSA. Quite why some don`t trust this, but trust everything else that the IET tell em` i really don`t know. :rolleyes:

No point in doing the maths if you`re gonna ignore the answer...
 
lol, you guys are going to hate me, but-

Do the same rules apply for a hob as a cooker? Obviously, the hob and cooker will normally share the same supply, but not always. How about an induction hob? I've just seen a hob rated at 6.7 kw.
I know its probably all in the regs/osg, but seeing as you like this thread so much.....;)
Also, whilst we are on the subject, if a cooker is physically incapable of drawing its rated current as electricAl pointed out, then er, why is that its rated current?! Surely, the manufacturers know how much current the cooker will draw, and put that on its rating plate, or is it just a question of them being safe (covering their backs),or lazy
 
Last edited by a moderator:

Reply to cooker diversity in the Australia area at ElectriciansForums.net

Similar Threads

Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
675
I'm interested what people's gut reaction solution would be. Kitchen design and customer said freestanding cooker. So I first fix 10mm, and boxes...
Replies
30
Views
3K
Hi all just here as an enthusiastic learner/diyer to gain knowledge and help on bits and bobs At the moment I am confused I have a new single...
Replies
20
Views
3K
Helloo guys, First post, so sorry if this is dreary! I'll try keep it simple... I have a client with a distribution circuit supplying AC...
Replies
4
Views
903
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock