Search for tools and product advice,

Discuss cooker diversity in the Australia area at ElectriciansForums.net

P

Peter Woodford

Guys,

bit confused on diversity can you help me out don't have regs book with me at mo

9000w cooker fitting 10mm cable so

9000/230 = 39.13 amps

how do i do diversity cooker has just a normal 45amp d.p switch what size mcb do i fit

cheers
 
Applying diversity to a cooker is as follows.

Take the full load, 39.13A.

Take the first 10A of this, add 30% of the remaining current i.e 30% x 29.13 = 8.73A

Total load after diversity = 10A + 8.73A = 18.73A.

Also if the control unit has a socket outlet incorporated then you add an additional 5A.
 
Lenny, do you (and others on here) always use diversity on a cooker, or do you er on the side of caution (ie you go up a cable/mcb size)? Only asking, as I often wonder what happens at christmas, when you've got a hob full of pans, and the oven going full blast trying to defrost the turkey!:D I guess if you didnt always apply diversity, cooker installs would be a bit more expensive with a 10mm.
Has anyone here ever installed a cooker circuit, applying diversity correctly, and run into trouble?

Just curious, as its always something I've wondered about.

Also, presumably you could just fit a 45 amp mcb (or more likely a 40), as the cable* and switch are rated for it?

* Presumably, may have to do a cable calc.
 
Last edited by a moderator:
MMM I went to look at a house this week and the owner had bought a 13.8 Kwatt cooker which equates to about 60 amps...scary.
Once diversity is applied then you come back down to about 28 amps I think from memory.
It dont seem right does it
 
Hi Peter

Why would you use diversity to size the MCB on a cooker circuit. Fit a 10mm cable subject to I meths and protect with a 40amp type b MCB.I would only be concerned with diversity when looking at the MD for the installation.

Regards
 
Last edited by a moderator:
But it is right to apply diversity - cos these things are designed NOT to draw their rated individual currents simultaneously, as in, the oven & the hob will simply not be able to be maxed out at the same time.
And the hobs cycle all the time - as soon as the reach the dialled temp, the thermostat switches them off, and on, and off...
The manufacturers KNOW this and thats why they suggest the CSAs that they do.

But if you want to do it your own way, nothing to say you can`t.

But a wise man once said, don`t bother buying a calculator if all you`ll use it for is hammering :)


p.s and whilst we should always design circuits correctly (if we know how, that is) a general rule of thumb for overloads is 1.45 With the exception of BS3036 fuses, all compliant protective devices are assured to trip in the required time at no more than x1.45 their In. The powers at be have made allowance for this when calculating the ccc of each of the cables listed in BRB
 
Last edited by a moderator:
[FONT=Times New Roman, serif]Hi Lenny, Al[/FONT]


[FONT=Times New Roman, serif]I'm confused how have you gone from using diversity on the sizing and then using 16mm² how have you come to this size?[/FONT]


[FONT=Times New Roman, serif]Regards[/FONT]
 
[FONT=Times New Roman, serif]Hi Lenny, Al[/FONT]


[FONT=Times New Roman, serif]I'm confused how have you gone from using diversity on the sizing and then using 16mm² how have you come to this size?[/FONT]


[FONT=Times New Roman, serif]Regards[/FONT]

By not using diversity. I must admit I will always cater for worst case scenario and go for the cable that meets the manufacturers rating, nothing worse than looking a fool when you have to tell someone on xmas day sorry but you cant use 2 rings of your cooker.:)

Protection wise I will usually look at diversity on that and go lower knowing that I have the back up if I need it as I installed a big enough cable.;)
 
Sorry Electro. We (or at least I) were/was just mocking our/we`re selves. The cooker question has been done quite a bit this week.

Back to your point....

As said, even with a outlet attached, when diversity`s applied the Ib (design current is genuinely and fairly assessed to be no greater than 24 amps.

So, as our In (rating of protective device) = or > than Ib the next common size would be Lenny`s 30A breaker (he should really have said 32A but he still thinks 3036s are new :p)

So Iz must be equal to or greater than In, so we`re looking for a cable (lets assume T&E is appropriate) so a 4mm would be ok in theory if a short, perfect run. As you must always check for VD :eek: you might even find the roughly...hmm...32 metres allowable for 4mm is too short.
But realistically, the run may not be wonderful old clipped direct C, so any factor applicable might well force you upto 6mm (very likely)
In the most onerous conditions, 10mm may well be needed - even if only to get you to sleep at night :D

Or if your running thru a foundy :cool:

But, seriously, if you apply the rules allowable you WILL come out with an appropriate cable size - and not an over engineered snake due to fear of the unknown.

Hope that does clarify it a little for you. If you want to know a little more on the subject of design etc - then i can recommend various references mate

& sorry for being silly before:eek:
 
Is that a serious question? :eek:
If i could tell you which cable to use for what, i could answer all the other people that ask me - and i can`t - so won`t.

I`ve tried to encourage you toward understanding that you can`t competently design a cct without all the relevant info. Anyone who can is a much better designer than me, or an idiot.

I gave you my answer - consider all the factors and use the next Iz rated cable up. I think thats quite within the capabilities of the average spark - it certainly should be.

Otherwise, stick a 16mm in on an 80A :rolleyes:

Tony Blair indeed :mad:
 
Hi electricAl

You have completely missed the point and tried to over engineer a situation that does not need to be over engineered. The secret behind design is knowing when to apply it and when you don't have to. Don't concentrate to much on volt drop in domestic, look more at the installation methods and loading. ElectricAl we will make a designer out of you yet.

Regards
 
Applying diversity to a cooker is as follows.

Take the full load, 39.13A.

Take the first 10A of this, add 30% of the remaining current i.e 30% x 29.13 = 8.73A

Total load after diversity = 10A + 8.73A = 18.73A.

Also if the control unit has a socket outlet incorporated then you add an additional 5A.


So does that.^^^;)
 
Are you guys being serious??
Generally cooker supplies go in at either 32 or 40 amps, there is nothing out of the ordinary with the cooker being installed so dont trouble yourself over this.
Read the onsite guide, its there for a reason and you will be well within the capability of a 6 mm cable, assuming the run is not overly long
 
...but obviously didnt trust the answer.

Obviously hes not the only one. But as Sparks1234 quite rightly said, we`ve been given ample guidance to arrive at a sensible CSA. Quite why some don`t trust this, but trust everything else that the IET tell em` i really don`t know. :rolleyes:

No point in doing the maths if you`re gonna ignore the answer...
 
lol, you guys are going to hate me, but-

Do the same rules apply for a hob as a cooker? Obviously, the hob and cooker will normally share the same supply, but not always. How about an induction hob? I've just seen a hob rated at 6.7 kw.
I know its probably all in the regs/osg, but seeing as you like this thread so much.....;)
Also, whilst we are on the subject, if a cooker is physically incapable of drawing its rated current as electricAl pointed out, then er, why is that its rated current?! Surely, the manufacturers know how much current the cooker will draw, and put that on its rating plate, or is it just a question of them being safe (covering their backs),or lazy
 
Last edited by a moderator:

Reply to cooker diversity in the Australia area at ElectriciansForums.net

Similar Threads

Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
693
I'm interested what people's gut reaction solution would be. Kitchen design and customer said freestanding cooker. So I first fix 10mm, and boxes...
Replies
30
Views
3K
Hi all just here as an enthusiastic learner/diyer to gain knowledge and help on bits and bobs At the moment I am confused I have a new single...
Replies
20
Views
3K
Helloo guys, First post, so sorry if this is dreary! I'll try keep it simple... I have a client with a distribution circuit supplying AC...
Replies
4
Views
919
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock