- Reaction score
- 362
Customer asking for a quote to re-vamp kitchen. Got some high end ovens/hobs:
Hob: 7.2kW
Oven: 3.7Kw
Steam Oven: 2.9Kw
Warming Drawer: 0.81Kw
She has told me other electricians have said another cable needs to be run for all this. Problem is that the CU is full, is build into a small cupboard, any new cable (SWA) would need to be run around the house - at least 30 meters. But I'm thinking the existing 6mm T&E on a 32A breaker is OK. To lighten the load could put the warming drawer on the ring.
Push comes to shove could up the MCB rating to 40A if install method allows?
Anything wrong in my thinking?
Hob: 7.2kW
Oven: 3.7Kw
Steam Oven: 2.9Kw
Warming Drawer: 0.81Kw
She has told me other electricians have said another cable needs to be run for all this. Problem is that the CU is full, is build into a small cupboard, any new cable (SWA) would need to be run around the house - at least 30 meters. But I'm thinking the existing 6mm T&E on a 32A breaker is OK. To lighten the load could put the warming drawer on the ring.
Push comes to shove could up the MCB rating to 40A if install method allows?
Anything wrong in my thinking?