HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought I'd ask the collective.

CU change today. I did my pre checks and I knew I had a major IR fault on the cooker circuit (N-E 0.3ohms, yes that figure is correct). The existing 30mA RCD was not tripping (have seen this before on a TT, @davesparks explained it to me and it makes sense). The RCD was fine, tripping within all parameters when all loads disconnected.

I realise I should have done the fault finding first, but I didn't. That will be tomorrow. Cooked circuit left disconnected for the night.

When I tested the RCBO (RCD test (x1 and x5 and ramp) ) on the cooker circuit by plugging in the tester at the socket on the cooker switch, the RCBO did not trip. When I RCD tested any other RCBO, the tested RCBO tripped and so did the cooker RCBO.

I'll track down the IR fault tomorrow, but can't get my head around why the above is happening?

Cheers in advance chaps (and SC and Julie)
 
A difficult one to explain but I'm pretty certain it'll stop once you locate and fix the cooker circuit IR fault, then testing that RCBO should have no effect on other circuits or vice-versa. Good luck !
 
As I understand your description, the cooker RCBO was connected to a circuit with an N-E fault, and it tripped simultaneously when any other RCBO was tested.

Traditional RCD test buttons (where there is no functional earth) test by transferring current from load L to supply N or vice versa, so they create an imbalance within themselves but not upstream, as no current actually goes to earth. Therefore, they won't interact with any other residual current sensing devices and would not cause this behaviour.

However, I think the test button in the RCBO you are testing dumps the test current to earth via its functional earth lead. As this is a TT system with significant Ra, instead of going to earth some of the test current diverts from the MET up the the cooker circuit CPC, through the fault, back down the cooker circuit N and through its RCBO to the supply neutral, causing an imbalance and tripping it. On a TN-C-S system this would not happen, as there would be a much lower resistance to earth from the MET, so the current would not divert via the cooker circuit.

It's kind-of the reverse situation to an RCD / RCBO trip on an N-E fault, when other circuits are carrying load. That causes the voltage on the neutral terminal to rise relative to the MET, due to the voltage drop along the main neutral, diverting current through the N-E fault. In your case the voltage on the MET is rising relative to the main neutral and the diverted current is flowing through the fault in the opposite direction.
 

Reply to Cooker RCBO trips when any other RCBO tested? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
733
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
327
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock