Discuss Critical feedback request - Consumer unit. in the UK Electrical Forum area at ElectriciansForums.net
Have you used ferrules on your RCBO fly leads?
Looks like the SWA is a 4 or 5 core.Looks neat,not sure of the actual workings of the system.
Where’s the bottom main switch fed from.
Yes that is true the bottom main switch is for the off peak supply feeding storage heater and immersionLooks like the SWA is a 4 or 5 core.
No none of the boards have ferrules I understand that is a requirement but my foreman will not listen.Does look good, be prepared to be ripped apart though
Have you used ferrules on your RCBO fly leads?
We are installing 200 of these board in a council estate. The cables on the left are being boarded .only thing i can fault is the bunch of cables coming in top left.some vertical plastic trunking would look better. otherwise a very neat job.
Thanks for your reply I agree with what you are saying. I have previously uploaded a past board from this job and received the same feedback. My foreman is refusing to purchase ferrules does not think they are needed.If the flylead is fine-stranded and has been cut and terminated in a terminal that is not designed for fine-stranded cable, then that is a genuine defect in the work. Bring your own ferrules or leave the full length of the flylead so you can terminate using the original crimped / spotwelded end.
I'm presuming you only need to add ferrules if you shorten the lead, or do you guys add them anyway?
show him reg. 526.9. ( from 17th . 18th. may be different number.).
No that is the tub strap box used for fixing the SWANice job
Why is there a piece of cardboard wedged down the back of the consumer unit ? Packing to get level ?
Yes your right thanks for the adviceYou need to colour identify you bottom neutral
Can't be arsed with arguing, but where does that **** come from?
17th Edition Amendment 3, 421.1.201 (ii)
states that consumer units shall be enclosed ...etc.
You can hardly call the CU enclosed if there's a gapping big hole in the back, especially as it's pointing at an easily combustable material such as wood.
The intent of that reg is to ensure the fire containment of the enclosure is maintained, which it isn't with a big hole in the back facing wood. It would be fine if it was mounted on a non-combustable wall, but it's not.
Think about it, what's the point of having metal enclosures, metal self closing doors over the mcbs, having to fit non combustable blanks, all designed to keep a fire within the CU, then a big hole that a fire can escape out the back of?
A couple of intumescent pillows stuffed in the holes will suffice.
It takes a real expert to do a messy install though ;o)))))Don’t fret, neatness comes with experience
Does look good, be prepared to be ripped apart though
Oh no! The BBC will be round to sort that......The breakers are leaning slightly to the right ;o))))
Bites tongue........Oh no! The BBC will be round to sort that......
The breakers are leaning slightly to the right ;o))))
I'm freshly back.
Reg 421.1.201, item (ii) refers to using a enclosure made from combustible material to be installed in a cabinet or enclosure made from non combustible material, i.e. comply with (i) or (ii).
MythBreakers videos - https://www.hager.co.uk/news-exhibitions-case-studies/news/amendment-3-to-bs-7671-2008/mythbreakers/56067.htm?mainvideoid=6dnZNI0bzRk
Unless they have changed the reg again in the 18th (I only have the BYB), there is no requirement to use intumescent seals in a CU made from non combustible material, only to maintain the IP ratings as per reg 416.2.1 (BYB). I don't believe the back of a CU requires this rating, although if someone could access the back, it would make common sense to maintain a similar IP rating.
Reg 421 etc actually says it shall "be enclosed in a cabinet or enclosure", I don't view having a large hole at the back as being 'enclosed'.
That video only stats that Hager, have done the tests, it doesn't cover all CU manufacturers, and he actually ends by saying "you may need to use some of these to maintain IP standards" (Intumescent seals etc.)
Normally I would totally agree with you but it's the fact that the material behind the hole is highly combustible i.e. wood and you have to consider External Influences i.e. BE2 - Fire Risks, characteristics required for 'erection' are equipment made of material retarding the spread of flame. Air, comprising that opening doesn't comply with that.
and CB2 - Propagation of Fire; erection characteristics required are Fire barriers, again air and wood aren't a fire barrier.
There's quite a large stand off gap between the CU and the wooden back board; if there was a fire in any of these CU's they're installing, air will get sucked in from around the CU and they'll be a blow torch effect out of the back of this hole, onto the wood, but if you still think that it complies and is no risk because the rest of the case is made of metal, then so be it.
Reply to Critical feedback request - Consumer unit. in the UK Electrical Forum area at ElectriciansForums.net