I did wonder that.If the conduit is metric, then presumably earthing nuts would fit the threads? Not sure that's of any help or not.
Is there a reason BS951 clamps couldn't be used to earth the conduit? This article from PE lists their intended uses, and kind of leads me to believe they would be okay for this:
Clamps, Earthing and Bonding: Correct Selection and Installation
BS 951 specifies the performance and important mechanical requirements for metal clamps that are used to provide mechanically and electrically sound earthing and bonding connections to metal tubes. Thetinyurl.com
No CPCs at any fitting - just live conductor singles pulled to each point - with the conduit acting as the earth...I am not clear as to whether you have an earth/cpc on the circuit, yes or no? So what you can do is cut the conduit back and use flexible conduit to go to the new box. That would need a cpc already in the circuit. If not then can you pull one in? As to the conduit being earthed, at the junction boxes such as where the lights are and inspection T's and 90 degrees etc you can put a fly lead joined to your cpc if this is not already done, secured with a round crimp and brass pan head screw. If there is no cpc then you need special tester to ensure continuity of the conduit earth. It puts out a high current and where the joins are it sparks if they are loose (forget what it is called) If this is not an option then you will have to draw in a cpc if you can access the inspection boxes??? Getting out the bushes requires a tool for the brass bush that you can buy at denmans. I have never found a jammed or impossible bush when doing this sort of thing but it does require the right tool. CK do one, bush spanner I would think it is called but it is not like a spanner. Oh and the best way to draw in an extra cable is to pull out the existing )one single and attach two singles taped on to the one you are pulling out.
Reply to CU replacement with earthed conduit and singles in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.