Discuss Damaged distribution circuit - repair or replace? in the Australia area at ElectriciansForums.net

Reaction score
14
What do you think? I've come across a damaged distribution cable while on another job, it's a 10mm t&e and there's a tiny bit of bare copper showing on the line. I immediately thought I'd run a new feed and replace it as the run's only about 12 meters but as the customer is complaining about having to spend out I'm wondering whether I could joint the cable in some way that would be acceptable above a false ceiling?

Do they even make choc-blocks big enough for 10mm cable? :D
 
Yes it will always be accessible. I wasn't too sure about using a junction box for a dis circuit but I suppose it should be ok, just not as tidy as pulling a new cable through. Would you minor works it and do an R1+R2 on the cable? Can't see it needs any more than that
 
Junction box should be ok as long as it is fixed, accessible and the cable sheath contained within.. I would also suggest an insulation test given the nicked wire, there may be other unknown damage to the insulation elsewhere.
 

Reply to Damaged distribution circuit - repair or replace? in the Australia area at ElectriciansForums.net

Similar Threads

I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
484
Hi guys, so I attended a property today where the lights were tripping with a neutral to earth fault. It turned out that a week previously the...
Replies
17
Views
3K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi, I'd really appreciate your help. This is in Europe. I have no electrical knowledge and very little construction/DIY knowledge. I know...
Replies
6
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock