Hello all, doing rewire at the moment and i have pit underfloor heating on dedicated ring to save cable. No reason why not right? Conductors in parallel and all that. Not using fcu's just using stat as DP isolator. 7 zones/stats. Design current ok with Ref method B. Am I doing the right thing?!?!

I heard a vicious rumour u can only use rfc's with sockets.

I can easily split it into 2x20a radials.

Thanks all.
 
You can use BS1363 accessories (e.g SFCU) in a ring final circuit. Not sure exactly what you are using here.
This is not conductors in parallel unless the conductors take the same route and are the same length.
It is a ring final circuit and should be tested as such.

Generally unless the layout is just so you are unlikely to save much cable, but it should be OK in general, albeit not very conventional.
 

Reply to Dedicated 32a2.5mm rfc for underfloor heating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi, I would like some advice on using Tado with electric underfloor heating to ensure it is I have Tado contolling my boiler and radiators...
Replies
6
Views
5K
Hello to everybody taking the time to read this post. I hope it is oK to post this here. I will start by introducing myself, I'm Martin from...
Replies
1
Views
1K
Here's one for a Sunday. I need some advice please. I went to quote for a job yesterday, where my client is replacing the aged electric convector...
Replies
10
Views
3K
Hi Guys New to forum and enjoying reading the threads, all interesting, so.. Looking to re-wire my kitchen due to re-fit and some of you will be...
Replies
64
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock