Search the forum,

Discuss Different core size connections in the Lighting Forum area at ElectriciansForums.net

Reaction score
7
Hi forum,
I’m planning some garden lighting and would like to try an minimise the amount of cable I’m using. I have a number of different lights/circuits in one area of the garden so was planning to run a multi core cable to a convenient place then make connections from there. All the lights will be LED and so very low voltage. Can I run eg a 12 core 1.5mm cable then Connect various 3 core 1mm cables to this? Or should the cable cross sections area all be the same?
Thanks in advance
Paul
 
connecting with wagos or connector blocks will be fine.
 
All the lights will be LED and so very low voltage.
Cable size is determined by current, not voltage. If you're using the cable to supply the light fittings with 12 Volts you need a much larger cable than the one upstream that's supplying 230 Volts to the power supplies/drivers.

I'd suggest you at least pay a sparky an hour for advice and help with the circuit designs even if you're going to do the installation yourself, I think it will work out cheaper in the long run.
 
Cable size is determined by current, not voltage. If you're using the cable to supply the light fittings with 12 Volts you need a much larger cable than the one upstream that's supplying 230 Volts to the power supplies/drivers.

I'd suggest you at least pay a sparky an hour for advice and help with the circuit designs even if you're going to do the installation yourself, I think it will work out cheaper in the long run.
Thanks for your replies, I couldn’t get hold of my electrician so thought I’d ask you guys. He also confirmed wago boxes will be ok so long as they are in a weather proof box.
 

Reply to Different core size connections in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
544
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
So, according to AS 3000 5.3.2 Earthing conductor material and type 5.3.2.1 Conductor material 5.3.2.1.1 Copper conductors Copper earthing...
Replies
2
Views
653
Hi Simple question I think - is there a specific cable requirement for connecting up 240v 6w LED downlights in a daisy chain extending the...
Replies
1
Views
1K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top