HI

I am not a professional electrician but have cabled all my houses since starting to build them 30 years ago. I know a dangerously small amount!

I am wiring my first 3 phase property in France and am looking for guidance on when to and when not to use a differential interrupter.

The two main items I am installing are a cooker and a Tesla charger both with 32A 4P interrupters.

Do either of them need to be differential please?

TIA,

Geoff
 
Others on there like @Mike Johnson will know a bit more about French regulations, as most folks here are UK based.

However, from what I believe practically all properties in France are TT earthed and will be fed by a time delay/selective RCBO ("differential interrupter") on the power company side that you have no choice over (other than the overload setting you get depending on your tariff). Thus if you don't have "instant" (normal) RCD per-circuit then a fault to earth will take out your whole supply.
 
Last edited:
Typical wiring diagram for a three phase to single phase domestic installation and the board.
DSC02263.jpeg
 

Attachments

  • Electric layout French 17-07-2022 Redacted.pdf
    176.3 KB · Views: 7
Last edited:
Pasted from a previous thread:

A source for everything to do with French electrics is here: Norme électrique 2013 2015, Amendement A4 normes NF C 15-100 - https://www.schema-electrique.net/norme-electrique-NF-C-15-100-amendement-A4-2013-2015.html#circuit-dedie Scroll to the bottom and a drop down list for most information is available.

On your browser go into preference's and change Language setting to always translate French.

Some of the differences:
1. No T&E all cable to have the same CSA, singles in flexible conduit is the norm.
2. Only eight MCB's to any RCD.
3.. All MCB's to be dual pole.
4. Most if not all white goods on their own circuit, as with extract fans, electric towel rails, Hob, Oven, etc: the list is quite extensive.
5. Not unusual to find a domestic installation is three phase.

This is a very good guide to French electrics: Amazon.fr - L'installation électrique - Gallauziaux, Thierry, Fedullo, David - Livres - https://www.amazon.fr/Linstallation-%C3%A9lectrique-David-Fedullo/dp/2416000055/ref=asc_df_2416000055/?tag=googshopfr-

NF-C 15 100 I think is the equivalent of the UK Blue Book, as far as I know there is no equivalent to any of our BS's.

Forgot to add "All power circuits are radials"
 

Reply to Differential v Non-Differential 4P Interrupter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Not an electrician and I currently live in an apartment building. Over the past few years I have been having abnormal problems with my...
Replies
2
Views
719
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
900
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
454
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock