Discuss Digital control of contactors in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
We are trying to control a bunch of 3 phase contactors using an HMI. The contactors' coils are activated by two lines of the 240V 3 phase source (L1 and L2).

We are trying to figure out if the relays needed for activating the coils should be rated at 120V or 240V, or if we need another type of relay.

We did a test with 120V relays(SSR) but one of the contactors' coil burned out after leaving it connected(OFF State) for about 3 days, we measured for current leakage on the relays but we didn't get any measure. We did another test measuring the current with a manual activation using a button an we get a reading of 70mA when contactor is ON.
 
Yea so the contactor coil is rated for 240V, but the problem was the relays that closes the line to power up the coil, as I think they are only rated for 120V. Could that have been the reason the coil burned out?
 
the problem was the relays that closes the line to power up the coil, as I think they are only rated for 120V. Could that have been the reason the coil burned out?

It's possible. If the control relays were SSRs, not rated for the 240V supply they were switching, it's possible that they failed short-circuit in one direction and fed pulsating DC to the contactor coils. I.e. the failed SSR looked like a diode as far as the contactor coil was concerned. Since a large part of the impedance of an AC contactor coil is its inductance, feeding it DC even of reduced mean voltage might result in excessive current and power dissipation.

Obviously this effect would not happen with a conventional relay, as this would be incapable of rectifying the current, but an SSR could easily do this.

Note to any other posters - the OP is in Mexico and the supply configuration is not 230/400V!
 

Reply to Digital control of contactors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I have a customer that has 3 heating mats under the tile. This was installed a while back and a relay was used. I measured a 21 amp draw for all...
Replies
4
Views
2K
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
618
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
998

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock