Steviet

Am I right In assuming that as long as you have worked out the fault current from a zr that meets regs for the breaker you can just use the disconnection time of 0.4 etc instead of using the graphs which I can never seem to understand
 
For example if I've got 32a bs60898 type by on a circuit of 0.55 zs this gives me 418A I can't seem to link this up to a disconnection time on the graphs I just don't get it aha
 
They are logarithmic graphs, that's why the scales are non-linear.
From left to right, starting at 1, the increments are 1 up to 10, then increments of 10 up to 100, then increments of 100 up to 1000, etc etc ...
For 418A, call it 400A, look at the 3rd line after 100, that's 400A.
Then look where the curve cuts that line, then the value on the time axis is your disconnection time.

BUT, a 32A curve is all to the left of the 400A line, so take the lowest time on the 32A curve as your disconnection time, that is 0.1sec


Hope that helps, but it's possibly confused you even more.
Blame my chronic explanation!!!
 
I think you have just made it make sense if my fault current doesn't match up to the curve of the breaker and its higher it'll be the lowest value of that curve and obviously it matches the curve it will then match up to a time higher than the lowest value. Now I'm sounding confusing but I think I understand it aha
 

Reply to Disconnect times for adiabatic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
When there is a fault on an EPS circuit, how are we meeting the disconnecting times? Earth fault is easy - just use a 30mA B-type RCD, but for the...
Replies
1
Views
877
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
888
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock