Currently reading:
Disconnected neutral wire from shower MCB in CU

Discuss Disconnected neutral wire from shower MCB in CU in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Good evening!

Recently, after a friend’s shower stopped working, an electrician allegedly disconnected the neutral wire inside the CU, to make the shower safe and isolate the circuit. Subsequently another electrician on visiting the house, unaware of this method (if it even exists!?) concluded that the shower itself was faulty and needed replacing. Consequently, the shower was replaced, but obviously didn’t work, and then having carried out a thorough check of the circuit, did he discover that the neutral wire in the CU was disconnected from the MCB.

And on opening up the new CU, which was only fitted a month before, it was apparent that the connections were hastily attached with copper wire showing protruding above the MCB connections and not neatly looped round as is (from what I understand) good practice. Indeed it seemed as though the wires from the old fuse box weren’t adjusted, but just forced into their new housings, and in all probability not attached with the appropriate torque settings!

So, could I ask if this is an acceptable method of isolating the shower circuit, and if it’s not there was it a potentially dangerous situation to have a loose neutral wire in the CU.

Any help much appreciated.

John
 
Good evening!

Recently, after a friend’s shower stopped working, an electrician allegedly disconnected the neutral wire inside the CU, to make the shower safe and isolate the circuit. Subsequently another electrician on visiting the house, unaware of this method (if it even exists!?) concluded that the shower itself was faulty and needed replacing. Consequently, the shower was replaced, but obviously didn’t work, and then having carried out a thorough check of the circuit, did he discover that the neutral wire in the CU was disconnected from the MCB.

And on opening up the new CU, which was only fitted a month before, it was apparent that the connections were hastily attached with copper wire showing protruding above the MCB connections and not neatly looped round as is (from what I understand) good practice. Indeed it seemed as though the wires from the old fuse box weren’t adjusted, but just forced into their new housings, and in all probability not attached with the appropriate torque settings!

So, could I ask if this is an acceptable method of isolating the shower circuit, and if it’s not there was it a potentially dangerous situation to have a loose neutral wire in the CU.

Any help much appreciated.

John

Strange to disconnect just the neutral. Ideally both conductors would be isolated.

You say the original electrician disconnected the neutral from the MCB though - now an MCB would not normally have a neutral terminal, but I wonder if is actually an RCBO?

Have you any photos?
 
Thanks DPG, for responding. And yes sorry, I probably got the terminology wrong. Attached is a screenshot of the photo I was sent.
As a layman, it occurs to me would it not be more commonplace for an electrician to remove the fuse from the shower pull chord switch, rather than switch all the house electrics off and go into the CU to disconnect the neutral wire? Anyway, your comments on the quality of wiring in the photo would also be most welcome.
Screenshot 2024-05-21 at 18.44.18.png
 
Last edited by a moderator:
It is probable that the black wire is not a neutral wire but that would have to be checked.

the photo shows that not a great deal of care has been used when fitting the new fuse box.

has the electrician mad the shower work now and provided you with a certificate?
 
I would expect at the least that the wires were correctly identified i.e. if the black wire is Live (going into a breaker) it should be sleeved or marked red or brown.
i would also expect some basic tests to have been done to confirm rcd times and earthing are within limits.
 
an electrician allegedly disconnected the neutral wire inside the CU, to make the shower safe and isolate the circuit.
Nope, no chance, I just cannot accept that, there is no way a proper electrician would just do that, something isn't right here, my 45 years experience tells me so.
 
Thanks DPG, for responding. And yes sorry, I probably got the terminology wrong. Attached is a screenshot of the photo I was sent.
As a layman, it occurs to me would it not be more commonplace for an electrician to remove the fuse from the shower pull chord switch, rather than switch all the house electrics off and go into the CU to disconnect the neutral wire? Anyway, your comments on the quality of wiring in the photo would also be most welcome.
There shouldn't be a fuse in the shower pull cord switch.

It could be that he disconnected both the Neutral and Live conductors in the consumer unit. ?
 
Thanks DPG, for responding. And yes sorry, I probably got the terminology wrong. Attached is a screenshot of the photo I was sent.
As a layman, it occurs to me would it not be more commonplace for an electrician to remove the fuse from the shower pull chord switch, rather than switch all the house electrics off and go into the CU to disconnect the neutral wire? Anyway, your comments on the quality of wiring in the photo would also be most welcome.
Can you take a picture so that the Consumer Unit can be seen.
 
Good evening!

Recently, after a friend’s shower stopped working, an electrician allegedly disconnected the neutral wire inside the CU, to make the shower safe and isolate the circuit. Subsequently another electrician on visiting the house, unaware of this method (if it even exists!?) concluded that the shower itself was faulty and needed replacing. Consequently, the shower was replaced, but obviously didn’t work, and then having carried out a thorough check of the circuit, did he discover that the neutral wire in the CU was disconnected from the MCB.
The first electrician disconnected the shower, presumably because it was faulty.

2nd electrician deems it to be faulty and is surprised when after he fits a new one that it doesn't work because it's been disconnected, something that you would expect to have been done ?? .

2nd electrician comments on how it should have been done best practice and all that good stuff.


So, could I ask if this is an acceptable method of isolating the shower circuit, and if it’s not there was it a potentially dangerous situation to have a loose neutral wire in the CU.
No electrician is just going to disconnect the neutral and leave the Live conductor connected.
The shower was probably causing a trip because of earth leakage.
 
Last edited:
From the picture I would hazard a guess that the red conductor was not long enough to reach the new MCB and has been extended with a bit of black conductor, not ideal but when it's the only option sometimes we have to do these things. Obviously it should have been identified red to avoid this confusion.

Something I make a point of teaching apprentices is to always refer to conductors by their colour and not their usual function, it helps to avoid falling into the trap of assuming that an incorrectly identified blue (or black in this case) conductor is connected to neutral.

If the OP had said the black wire has been disconnected and shown us that picture I think a lot more people would have seen the likely scenario of using a black wire to extend the red.
 
As a layman, it occurs to me would it not be more commonplace for an electrician to remove the fuse from the shower pull chord switch,
They don't contain fuses, they are just a switch.
rather than switch all the house electrics off and go into the CU to disconnect the neutral wire?

I doubt that is the neutral wire, it is more likely a live which has been extended using a bit of black.

Anyway, your comments on the quality of wiring in the photo would also be most welcome.

It is not ideal and could be improved, but you also can't expect a picture perfect, Instagram worthy, CU from that without jointing and extending all of the conductors. Obviously it would look a lot nearer if you did that, but you would also have introduced a potential point of failure into every conductor for the sake of asthetics
 
Recently, after a friend’s shower stopped working, an electrician allegedly disconnected the neutral wire inside the CU, to make the shower safe and isolate the circuit. Subsequently another electrician on visiting the house, unaware of this method (if it even exists!?) concluded that the shower itself was faulty and needed replacing. Consequently, the shower was replaced, but obviously didn’t work, and then having carried out a thorough check of the circuit, did he discover that the neutral wire in the CU was disconnected from the MCB.
Being honest this all sounds like a series of red herrings to me.
The original sparks disconnected shower for a reason, presumably because they had grounds to believe it was faulty or dangerous.
The 2nd sparks fitted a new shower and after some confusion made it work.
Good result?

Without before and after photographs you're never going to prove the 1st sparks did anything wrong, and it sounds as though the 2nd sparks could be criticised for lack of testing before and after attempting to energise the shower circuit.

I don't see what any further action can achieve, other than getting someone competent to check over and tidy up that consumer unit a bit.
 
Being honest this all sounds like a series of red herrings to me.
The original sparks disconnected shower for a reason, presumably because they had grounds to believe it was faulty or dangerous.
The 2nd sparks fitted a new shower and after some confusion made it work.
Good result?

Without before and after photographs you're never going to prove the 1st sparks did anything wrong, and it sounds as though the 2nd sparks could be criticised for lack of testing before and after attempting to energise the shower circuit.

I don't see what any further action can achieve, other than getting someone competent to check over and tidy up that consumer unit a bit.
 

Reply to Disconnected neutral wire from shower MCB in CU in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock