Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant.

We had wired it with 10sq and 40a RCBO.

10sq Neutral cable looping from neutral bar to RCDs and on to shower RCBO melted at neutral bar.

That's fair enough, must have been pulling a fair whack through it.

So I put in a new 10sq neutral going straight from neutral bar to shower RCBO.

They say the smell is back again.

I think the installation is pulling way over 63amps, when shower, cooker, dryer etc is on.

It's fed through a 100a double pole isolator, should I swap this out for a 63 amp MCB to cover my arse
 
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant.

We had wired it with 10sq and 40a RCBO.

10sq Neutral cable looping from neutral bar to RCDs and on to shower RCBO melted at neutral bar.

That's fair enough, must have been pulling a fair whack through it.

So I put in a new 10sq neutral going straight from neutral bar to shower RCBO.

They say the smell is back again.

I think the installation is pulling way over 63amps, when shower, cooker, dryer etc is on.

It's fed through a 100a double pole isolator, should I swap this out for a 63 amp MCB to cover my arse
63A MCB will not trip off at exactly 63A... can take a bit more, for some considerable time. Same with the 40A RCBO.

Do you have the measured voltage? As 9.8kW / 230 is 42.6A... over your 40A

Depending on installation method, its on the limit of 10mm cable now.

If the link cable at the neutral bar was melting, then more likely a loose connection than undersized cable.
Did you use a different terminal hole? The one that had the melted cable originally in it may have carbon deposits, which is now causing the smell, and still possibly heating up.
 
As above, if it's overheating at the joint the it's most likely the joint. With the short length of time a shower is on for I can't see the 10mm cable itself overheating.
 
Last edited:
I've seen a 10kw shower survive many years on 2.5 sq mm cable which is obviously not compliant but does illustrate that this issue is unlikely to be the cable size (and the 10 sq mm might be compliant, as per above).

Did you change the B40 RCBO after this happened or splice onto the Neutral fly lead of the old one?
Also as above, I'd take a good look at all connections.

It's fed through a 100a double pole isolator, should I swap this out for a 63 amp MCB to cover my arse
A B63 MCB won't trip at all until about 90 amps is flowing and then it would take over 2 hours before it trips. I really can't see that idea helping this situation at all.
 
I swapped neutral bar out completely, it was well shagged.

I also brought a 10sq neutral straight from shower RCBO to neutral bar.



I'll attach some pictures.

Second one is the load on the shower neutral after I replaced it and ran it direct to the shower RCBO

Obviously couldn't tell if cable was loose at that stage but tightened up everything so should be ok now.



PXL_20230610_113654434-min.jpg
PXL_20230611_080043137-min.jpg
 
Last edited:

Reply to Shower and load on board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So abit of a random one. But yesterday my Neighbor asked me if I'd be able to take a quick look at their shower as it had stopped working. I said...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock