Discuss Wiring 50amp outlet, but only 3 wires run to the disconnect in the UK Electrical Forum area at ElectriciansForums.net

Rrands1

DIY
Reaction score
2
I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3 wires run to it - hot, hot, and ground. I want to repurpose it for an RV hookup, using a Nema 14-50R receptacle. However, that receptacle requires a neutral, which is not present in the disconnect. I know my RV also does not really use 220, but just 110, so a neutral will be required.

my question is: at the receptacle enclosure, can I tie the ground and neutral together, using the ground as a neutral as well?

if not, is it possible to “repurpose” one of the hot wires into a neutral, and just have this be a 110 circuit? (At which point I would use a TT-30 R receptacle). At the service panel, I would change to a single pole breaker, and move the old hot wire to the neutral bus. But if that is allowed, since the wire color is different, should I wrap it in white tape or something? And would it matter if it were the red or black wire at that point?

for other reasons, I really prefer the 14-50R outlet if that is possible!


thanks for the help!
 
I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3 wires run to it - hot, hot, and ground. I want to repurpose it for an RV hookup, using a Nema 14-50R receptacle. However, that receptacle requires a neutral, which is not present in the disconnect. I know my RV also does not really use 220, but just 110, so a neutral will be required.

my question is: at the receptacle enclosure, can I tie the ground and neutral together, using the ground as a neutral as well?

if not, is it possible to “repurpose” one of the hot wires into a neutral, and just have this be a 110 circuit? (At which point I would use a TT-30 R receptacle). At the service panel, I would change to a single pole breaker, and move the old hot wire to the neutral bus. But if that is allowed, since the wire color is different, should I wrap it in white tape or something? And would it matter if it were the red or black wire at that point?

for other reasons, I really prefer the 14-50R outlet if that is possible!


thanks for the help!
If all you really want is 120vac then yes you can use the red or black and tape it white to be your neutral. As far as the 240vac you would need to pull a neutral or white wire. Good luck
 
Thank you, I appreciate it! I think I will just run the neutral - extra work, but helps future proof, too... :)
If the feed is NM cable "Romex®" you will need to pull a new cable from panel, if is in pipe it might be possible to add a neutral but might not be easy, just running a neutral by it's self will not be code compliant.
 
If the feed is NM cable "Romex®" you will need to pull a new cable from panel, if is in pipe it might be possible to add a neutral but might not be easy, just running a neutral by it's self will not be code compliant.
thanks, all - I ended up pulling the 3 wires back out of the conduit, adding a 4th (neutral) and re-pulling - works great! :)
 

Reply to Wiring 50amp outlet, but only 3 wires run to the disconnect in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

we just replaced our hot water tank with hot water on demand (natural gas) and still have the old power run for the tank which is 30a 240v. I...
Replies
1
Views
2K
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
834
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
467
I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the...
Replies
5
Views
2K
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
440

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock