Hi all

im sorry ask such a stupid question but I seem to be having a moment as I can't think straight today but what's the safe distances you can put accessories near a boiler?

Thanks in advance
 
512.2.1 equipment shall be of a design appropriate to the situation in which it is to be used or its mode of installation shall take account of the conditions likely to be encountered.

528.3 proximity to non-electrical services

BS 6891 installation of low pressure pipework in domestic premises, clause 8.16.2

Where gas installation pipes are not separated by electrical insulating material from electrical equipment, including cables, they are to be spaced as follows:



  1. At least 150 mm away from electrical equipment.
  2. At least 25 mm away from electricity cable.

Last but not least the manufactures instructions should be taken in to account for both the boiler and accessory you wish to install. For example if installing a wireless receiver for a room thermostat next to the boiler the manufacturers instructions of the receiver will normally specify a minimum distance because of interference etc.
 
Last edited:
Thanks for the response

the boiler is in the kitchen and the client wants a double socket right next to it which I have informed them that you cannot, but someone has installed the SFS right next to the case.
 
From the case or from the pipework?

I agree with 150mm from pipework (if possible, but definitely from gas)
I would be willing to put it a bit closer to the case if I REALLY had to.

I have seen many a boiler where the plumbers have modified bits so that their pipework covers accessories etc.
 
I agree 150mm as good practice and belt and braces for your own back, but just to put the cat amongst the pigeons, what about the flex entry to the boiler, how any installations do you see where the 25mm rule from the gas supply is ignored or almost impossible to avoid...
 

Reply to Distance to boiler in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
826
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
993
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
434
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock