Hi
I have a question regarding switch boards and distribution boards. We have an existing switchboard and we want to use four spare ways in this to feed three new tp & n distribution boards. One for lighting one for small power one for security services. My question is what calculations have to be performed to ensure the new boards will operate from the existing switchboard?

Thanks
 
Thanks. It seems simple enough but what I not need to calculate prospective short circuit fault current and other parameters or am I being silly?
 
Thanks. It seems simple enough but what I not need to calculate prospective short circuit fault current and other parameters or am I being silly?
 
Hi - the protective device for the new circuits must still meet the requisite ADS time. So the usual combination of mcb rating and max EFLI need calc.
 
Hi
I have a question regarding switch boards and distribution boards. We have an existing switchboard and we want to use four spare ways in this to feed three new tp & n distribution boards. One for lighting one for small power one for security services. My question is what calculations have to be performed to ensure the new boards will operate from the existing switchboard?

Thanks
Are these spare ways, TP or SP?
 
Of course the normal cable calcs apply after you have worked out the capacity and demand.
Thanks. It seems simple enough but what I not need to calculate prospective short circuit fault current and other parameters or am I being silly?
 

Reply to Distribution board checks in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
287
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K
Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
Replies
2
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock