Discuss Do maintained emergency lights in communal area need keyswitch in the UK Electrical Forum area at ElectriciansForums.net

E

Eddiesparks

This sounds like a daft question but i am doing an install that requires lighting in the common area and of course emergency escape lighting.

I am thinking of installing something like this which I assume requires a perm live, a neutral and earth to each (can't see a need for three core plus earth for these but maybe I am wrong! The integral sensor means they only need a perm live right?!

They have integral sensor so they come on when people go near them and they also work as emergency lights. My question is firstly, have i got the above all correct and also would i need a keyswitch at source to test them (surely the mcb would do the same job in this case?!) or would you know they are working because the lamps are working in normal operation.

Apologies for my ignorance in this,

https://www.tlc-direct.co.uk/Products/LTPMESW.html

Thanks people
 
I would always put a keyswitch... many buildings use self testing procedures and many places won't allow their staff to enter electrical boards or switchrooms so a separate key switch is, in most in cases the best option from what I have come across so far.
 
Totally incorrect.....Easiest way to do this is using 3 core T+E. From db take 2 core T&E to em test switch, then to first pir sensor. From then on 3 core T&E to every polo fitting weather em Polo or just normal polo fitting, and into every additional pir sensor on the circuit. Each pir sensor will be perm L, N & SWL, each em Polo will be L, N & SWL, every non em polo will be L linked, and SWL, N connected.
 
ok it cant hurt can it really?!

More importantly do i have the wiring right then: T&E from CU to keyswitch, T&E from keyswitch (single pole, neutrals joined - "2 plate style") to first light, T&E from first light to 2nd light etc?
 
Yes it can, without constant L, the Polo will stay lit and the batteries will discharge.....??
Are your sure your up to doing this life saving work...?
 
Hopefully this will explain better.
Em Lighting.jpg
 
tazz you misunderstood me, didnt see your post before my 2nd one.

I was saying couldnt hurt to put keyswitch in.

Regarding what you say - i am installing 5 polo emergency fittings only, they have integral sensors so no need for external PIRs in my understanding. I understand full well that with external PIRs you need to use three core for PL,SL and N. And i understand what you are saying with linking perm lives in non emergency ones etc.

From my questions it is clear i am not a complete muppet, i do know a bit about this and i am well aware to leave things alone which i am totally clueless about but not installed an emergency fitting of this type with integral sensor before.

Do you see where I am coming from on this?! try and be nice - i am just asking a question mate
 
ps thanks for the diagram, as i said i do understand that but I am unfamiliar with sensor switched emergency fittings. Perhaps i am misunderstanding what the light i put a link to actually does?
 
As I understand it there won't be a functional switch in the circuit apart from maybe a keyswitch for testing (by doing this you're testing the batteries, not the lamp). The switch would effectively be the PIR, which is integral to the fitting, so you'd only need a permanent live going to the fitting. If the fitting needs a secondary live you could link out the permanent live in the fitting.

The only thing you might want to consider is putting them on 2 separate circuits so when you test one there is still light in the corridor.
 
Sorry, now you have explained, yes I do....Have used polo`s alot in nursing homes....but now I see the built in sensors, which I not a fan of, due to individual lights coming on instead of complete corridors or sections. Personally I would use separate pirs on entrance areas, and buy polo standard units. The polo`s are good units, here`s a photo of them in operation.
2013-09-17 19.22.35.jpg
 
Sorry, now you have explained, yes I do....Have used polo`s alot in nursing homes....but now I see the built in sensors, which I not a fan of, due to individual lights coming on instead of complete corridors or sections. Personally I would use separate pirs on entrance areas, and buy polo standard units. The polo`s are good units, here`s a photo of them in operation.
View attachment 28175

Did they replace 1200x600 recessed fluorescents by any chance?
 
Actually No, the replaced 14 month old D fittings, which kept failing and burning out.....I don`t know why the ceiling tiles are mismatched.....The reason I didn`t use internal sensors, was so each of these long corridors would come on in complete sections, with no blind spots.
 

Reply to Do maintained emergency lights in communal area need keyswitch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
646
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
876
Hi So I'd like a maintained emergency light but without the automatic emergency function to trigger in the event of power failure. In other words...
Replies
11
Views
2K
Hi all Got a question regarding HMO compliance. Visited property today for landlord looking to apply for an HMO license for one of their...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock