And in the final bit of my project of this part is to pick protective devices for the hotel block.
There isn't that much info on the hotel block but the info I have been provided with is as follows: "The existing hotel building forms part of an 400V three-phase TN-C-S system...A new CCU will be installed to supply the distribution circuits. Ze is 0.09 and PFC is 5kA" - There are 8 distribution circuits to feed 8 sub boards, each board then feeds 2 rooms- each room has 1 socket circuit , 1 air con supply and I'm assuming one lighting circuit although the spec hasn't stated it. There is no information on what cables will be used and how they will be installed(as with the café block in this project I was provided with this info).I was going to use RCBOs in the sub board and then 3 pole MCBs to supply the sub boards and I'm confused to whether these distribution circuits need RCD protection. If they do need RCD protection then I will put a 100ma RCD to protect these distribution circuits as I know I would need the 3:1 ratio with the other RCD devices(RCBOs in sub boards) and the RCBOs in the sub boards are going to be rated 30mA so if a fault happens in any of the circuits in the sub boards it then doesn't trip the RCD protecting the distribution circuits. But if no RCD protection is needed for these distribution circuits then I will just have the 3 pole MCBs on their own. Am I right in thinking this ?