Would appear BS and Scottish government are not 100% in sync.
Guess Scottish government position is that having smoke alarm(s) whether it's mains or battery powered is better than not having any at all.
On a separate note, if I bought every BS standard that I would touch upon, then storage of these alone (forest of paper) would results in an increased fire risk
They are not in Sync, but the Scottish rules go beyond the UK.
F2 is not permitted for any mandatory detectors - but can be used for additional.
The minimum quantities under BS5839 are not sufficient under Scottish law.
The law in Scotland is that EVERY home MUST have interlinked alarms:
Main living room
Each circulation space on every story
Kitchen (Heat)
CO in every room with fossil fuel device (boiler/fire etc) or containing a flue.
ALL sensors must be ceiling mounted
Not just new builds/modifications - however F1 is considered acceptable.
BTW, alarms from different circuits cannot be interconnected, only via wireless in these cases.
You could interconnect say all the alarms on each story and just have one wireless on each circuit connecting to the other circuit.
Wouldn't be ideal but has been accepted in Scotland.
The law is here:
Fire and smoke alarms: changes to the law
The law on fire alarms has changed which means all Scottish homes will need to have interlinked alarms. Guidance on what you need to know.
www.gov.scot
A Typical older house would require
3 x smoke,
1 x heat
plus:
CO in the Boiler location
CO in the front room (Gas fire)
CO in the Living room (Gas fire)
CO in the front bedroom (The flue from the downstairs gas fire passes through)
CO in the Rear bedroom (The flue from the downstairs gas fire passes through)
All either mains powered, battery back up interconnected, or 10 year battery with wireless
Scottish government expect this is £200