Double insulated down lights cpc

Discuss Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

94E4DDFB-0368-4B1E-98C0-81BC1A837D67.jpeg
 
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
obviously wago'd into the other cpc where ther are 2 cables?????
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
What do you suppose cpc stands for.
 
I'd still contend, that in the case of a CPC feeding a single luminaire, that it is not a "protective conductor" as the CPC is not linking Exposed Conductive Parts, if it were the CPC would be connected to the accessory, and therefore there is no requirement to enclose.
 
What do you suppose cpc stands for.
There are protective conductors and Protective Conductors.

Other than the instance highlighted above the CPC does not fit the definition on P33 and is not specifically listed as an example.

It is their for fault protection not electric shock protection.

So, as i read it, a CPC can be but is not always a protective conductor.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net