Double insulated down lights cpc

Discuss Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

94E4DDFB-0368-4B1E-98C0-81BC1A837D67.jpeg
 
This is not an exercise in what I consider but what the book stipulates.

Please try to stick to the discussion rather than trying to undermine contributors.
Not what I am doing but you have stated the cpc is not a protective conductor although cpc stands for circuit protective conductor.
 
Not what I am doing but you have stated the cpc is not a protective conductor although cpc stands for circuit protective conductor.

No 'I' haven't. I have said that the book does not include CPCs as Protective conductors, and it is very specific as to what is does include.

Why does it not specifically refer to a CPC as a Protective Conductor?
 
No 'I' haven't. I have said that the book does not include CPCs as Protective conductors, and it is very specific as to what is does include.

Why does it not specifically refer to a CPC as a Protective Conductor?
You are looking for something which is not there, I could be incorrect but BS7671 does not use the abbreviation cpc. I believe it is only in the definitions in brackets after Circuit Protective Conductor.
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
A cpc is relevant to (i).
 
All/most of the LED commercial downlights we fit have drivers that only allow one 0.75mm 2 core flex. Mostly we have plug-in LCM boxes and can wire flex to the plug if it is an MF plasterboard ceiling we use Click-Scholemore flow connectors.
 
It is not permitted for Class 2 items to have an earth connected to them.
I take the view that if you are looping in and out of fittings this is part of the circuit and should have a CPC and that where there is the final connection to a fitting not requiring an earth eg double insulated etc. it is permissible to use two core flex.
 
So does that mean that this class 2 cheap screwfix light does not meet regs as it has made no cpc termination or allowance for terminating cpc within the enclosure.

412.2.3.2 Except where Regulation 412.1.2 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.


NOTE: This requirement is intended to take account of the replacement by the user of Class ll equipment by Class I equipment.


All depends on how you interpret it.
It doesn't say how it should be "terminated at each point in wiring and at each accessory."
Unusual for the regs not to be clear...... Go figure......
 
As I have already suggested, the solution is to strip the CPC back so that it can be terminated outside of the enclosure.

The minimum CSAs of 2.5mm2 and 4mm2 are not applicable as the CPC forms part of a multi core cable.

There is no requirement in BS7671 for terminations to be made within an enclosure.
However there is a requirement for this CPC to be terminated at the accessory.
 
As soon as you strip the cpc back and put it outside the enclosure it is no longer contained within the cable sheath and hence Reg 521.10.1 would come into play.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock