Ok so I'd like your opinions on this as I seem to be the minority on this.

I'm fairly newly qualified and obviously still learning everyday.

Electricians I work with and everywhere on the web says that spurring a double socket from another that is on a ring final circuit is fine, as long as it's just the one!

Ok so let's set the scene, one double socket spurred off of another via 1x 2.5 t and e, the source socket used is in a ring final circuit on a 32a mcb.

With my understanding 1 single 2.5mm t and e has a ccc of say 27a ref method c, so you could potentially plug 2x 3kw heaters into your spurred socket on full power and thus over load the cable but not the mcb causing potential danger ??

I know any danger is highly unlikely as you'd nearly never plug anything in to draw such a load but surely the potential to is enough for this not to be good practise ??

I must be missing something as everything and everyone I ask seems to say it's fine but surely you'd just extend the ring circuit or add a fused spur first before the additional socket ??

thoughts?

TIA.
 
And it would be more than highly unlikely that two appliances consuming 3kW each would both be plugged into the same double socket and/or running simultaneously.
 
Ok so I'd like your opinions on this as I seem to be the minority on this.

I'm fairly newly qualified and obviously still learning everyday.

Electricians I work with and everywhere on the web says that spurring a double socket from another that is on a ring final circuit is fine, as long as it's just the one!

Ok so let's set the scene, one double socket spurred off of another via 1x 2.5 t and e, the source socket used is in a ring final circuit on a 32a mcb.

With my understanding 1 single 2.5mm t and e has a ccc of say 27a ref method c, so you could potentially plug 2x 3kw heaters into your spurred socket on full power and thus over load the cable but not the mcb causing potential danger ??

I know any danger is highly unlikely as you'd nearly never plug anything in to draw such a load but surely the potential to is enough for this not to be good practise ??

I must be missing something as everything and everyone I ask seems to say it's fine but surely you'd just extend the ring circuit or add a fused spur first before the additional socket ??

thoughts?

TIA.
Suggest you familiarise, yourself with Appendix 15 Regulation 433.1.204 Fig 15a 17th edition page 453, gives you all the information you require I should think.
 
you've answered you own question, the 2.5mm cable (27a rating) serving the spur will not be overloaded by two 13a appliances (26a).

Ok so that does make sense and I knew it was something simple I was missing, however what if they had an extension lead plugged in and had something else plugged in pulling another 1kw putting the load to 30a ?

I know this is ridiculously unlikely but it's still possible, if this happened could it start a fire then you'd be at fault and liable ?


you've answered you own question, the 2.5mm cable (27a rating) serving the spur will not be overloaded by two 13a appliances (26a).
 
Even if both points of the socket outlet were drawing 13A it would be an extreme installation method which would result in the cable combusting (Is that a word?)
 
Ok I agree BS1363 four hours 14a 6a and so on. But somehow I doubt it really especially on cheaper sockets. Maybe MK and some others but In a commercial kitchen I was working in where they are running loads of 3kw items and for at least several hours a day, it is hard to whole heartedly advise that is OK. But then I suppose we are talking domestic. And anyway I think they should have had a single socket for each appliance.
 
I agree we used to work for one of the leading fast food outlets, chicken to be precise and they had multiple radial 13A points for individual appliances. You could have six sockets at one point covered by six circuits.
 
Hi CFTIS
A bit of a digression, but the vagaries of RFCs are something which have annoyed me for decades. I personally think they are obsolete now that WWII is over and copper is plentiful, but it appears I'm in a minority here.
See this thread for details:
Can I join 2 radials to make a ring? - https://www.electriciansforums.co.uk/threads/can-i-join-2-radials-to-make-a-ring.123486/
I always enjoy splitting rings at the furthest point and converting them to 2 x 20A radials.
I believe rings are potentially dangerous after only a single (and common) point of failure (ring break). It's the same intuition that made you question the (regulation-acceptable) issue of daisy-chained spurs on a 32A breaker. Well done for obviously thinking it through.
We will now get replies saying that no one would ever plug multiple 13A loads into a single ring. Sure, that may be true, but if we assume it is always true, why then do we ever need to protect plug outlet circuits at 32A? That's my point. You can't have the argument both ways! (And I'm assuming good installation practice with no heavy fixed loads - eg immersion heaters - spurred off the ring.)
I hold that just because the regulations say that something may be done in a certain way does not ALWAYS make it the best, or even the right, way in every situation. And the converse is also true :)
 
Last edited:
Hi CFTIS
A bit of a digression, but the vagaries of RFCs are something which have annoyed me for decades. I personally think they are obsolete now that WWII is over and copper is plentiful, but it appears I'm in a minority here.
Each to his own...
 
I suspect this has been done many times before, but given that the CPC is smaller than the others in T&E, it may be more prone to damage. Therefore an O/C live conductor in a ring is less likely than an O/C earth in a radial, and equally unlikely to be noticed. It is then arguable whether the typical loading on a broken ring (effectively two radials) is more likely to cause danger by exceeding the rating of the cable than the lack of an earth on a radial past the broken part.
 
... It is then arguable whether the typical loading on a broken ring (effectively two radials) is more likely to cause danger by exceeding the rating of the cable than the lack of an earth on a radial past the broken part.
That's a very good point which I admit I had never thought of before.
That rings have - by accident - what is effectively a high integrity earth is useful, but not useful enough to convince me to use them, unless protected at 20 or 25A (which I have occasionally done.)
Your point about an unnoticed broken earth applies of course to all types of circuit.
 
I have wondered why the mcb/rcbo makers have not yet made a specific breaker for the ring circuit ...
Probably because there's little market outside the UK.
I once installed some RFCs, using UK sockets, in Asia, but could not get the local contractors to understand why they were wired like that. They were completely puzzled, and thought I was a madman. :)
 
why then do we ever need to protect plug outlet circuits at 32A

Diversity & flexibility. Suppose you have three 2.4kW loads (this is an artifical case to illustrate, I accept it is stretching the point, but 3kW appliances are not as common as they used to be). You can plug them all in anywhere on a 32A circuit without further thought. With 2x 20A although you have 8A more available in total, you can't plug those three loads in anywhere without technically overloading one circuit.

The 32A vs. 20A debate is a separate consideration to the ring vs. radial debate, as you can have 32A radials which might be the best of both worlds.
 
Marconi's idea is to not connect the ends directly at the DB, but to insert a measurement shunt or balance transformer winding of low resistance, that can detect the current flowing in the two legs separately, or inject a tiny measurement current that flows around the ring. This would allow the breaker to detect an open-circuit in the ring even while all the connect loads can still see L, N & E. It wouldn't work reliably for the CPC though, as there may legitimately be parallel paths to various points that bypass the detection circuit or disturb its balance.

You could make a simple detection scheme for the L & N, that would respond to one conductor being broken, using a low-sensitivity balance transformer added to an ordinary RCD. One leg would be wired through it and one would bypass it, so that it would only see balance provided the current in L and N divided between the legs in the same ratio. Any single break would change the division ratio in that conductor but not the other, causing the detection transformer to trip the breaker. An ordinary balance transformer would still be needed in the unit to provide shock protection. It would not detect both conductors broken in the same place, as the two disconnected legs would inherently be in balance again.

Kitchen table project for Marconi... Mock this up using a 4-pole RCD. Both legs through poles 1 & 2 for shock protection, one leg only through poles 3 & 4 as well for ring break detection. Adjust sensitivity and trim balance by shunting poles 3 & 4.

FWIW some of the early lamp failure detection schemes in cars used the difference in currents between left and right circuits to trigger the warning with a differential relay. Both lamps out would not be detected.
 
... Suppose you have three 2.4kW loads (this is an artifical case to illustrate, I accept it is stretching the point, but 3kW appliances are not as common as they used to be). You can plug them all in anywhere on a 32A circuit without further thought. ...
Indeed you can, and that's exactly my point: if one ring conductor is open circuit, you then have a potential (and entirely invisible) cable overload, especially at the far end of long rings.
I agree both our arguments are stretching the point, as I don't believe many people do actually plug in multiple 2.4kW / 3.0kW loads any more. But if that's so, one doesn't need the 'flexibility' of 32A.
 
Indeed you can, and that's exactly my point: if one ring conductor is open circuit, you then have a potential (and entirely invisible) cable overload, especially at the far end of long rings.
I agree both our arguments are stretching the point, as I don't believe many people do actually plug in multiple 2.4kW / 3.0kW loads any more. But if that's so, one doesn't need the 'flexibility' of 32A.
It's the middle of winter and minus 5 outside, your boiler breaks so off you go to find some 2.4kW heaters to keep your family warm. You have 2 , you borrow another 2 off a mate....
 
Probably because there's little market outside the UK.
I once installed some RFCs, using UK sockets, in Asia, but could not get the local contractors to understand why they were wired like that. They were completely puzzled, and thought I was a madman. :)
It will never work Mr Pete:confused:
 

Reply to Double socket spurred off of Ring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
789
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
316
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
763
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock