Discuss Downlights in the UK Electrical Forum area at ElectriciansForums.net

A

Adie

Hello i am in the process of fitting three downlights but there is no earth connection on the lamps,i have run the switched live neutral and earth into a junction box in the loft and than fed x3 1.5mm twin earth to each lamp but not sure if it is alright to terminate the earth wires in choc box at each lamp or do all the earths need to be joined together.
 
As a bus driver the op probably doesn't know what loop in loop out means... To op please get a local electrician to come and help you
 
Picture of the lamps.? Why have you run each one individually to a junction in loft and not loop in/out @ each fitting?
Hello,i have run them into a junction box as the electrical connectors on lights is quite compact and thought it might be easier to run individual cable to each light,is the best method to loop in and out and than park the final earth cable in a choc box.Thank you for your reply.
 
As the fittings are class II, then terminating the cpc in the lamp connector block is OK, at the remote junction box the cpcs should be joined to the supply cpc so that an earth is run to each point (light fitting) in the circuit even though it is not required for the light fittings you show.
 
What Mr Burns said above ^^^^
Out of interest, what junction box are you using?
 

Reply to Downlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight...
Replies
55
Views
5K
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
921
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
552
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock