Piratepete

Hi Guys
I fit a lot of IPX5 and IPX6 accessories and wonder if I should be drilling a drain hole at the spot that's usually indicated. Most have instructions that have no guidance except to say that the IP rating will be compromised if you drill a drain hole.
However the instructions with a make (rated IP55) new to me say that a drain hole is required if cables are glanded from the top or side and also if the bottom entry gland completely seals!

The question has added urgency since opening an IP66 adaptable box I installed some years ago (with side entry) and finding it half full of water! I 've always doubted whether the standard compression glands seal on flat cable. The downside for drain holes is they let the wee beasties in.

What do you do? Is there guidance anywhere on this? Started putting a blob of silicon at the gland entry now!

Cheers
Pete

PS. Whats a good way to fit a weatherproof double socket to a vertical steel column without drilling it? Any suitable clips around?
 
We always drill a small drain hole in bottom of any any external connection enclosure even floodlights as seen them fill with water so many times.
The factory seals on most enclosures do not seem to be up to the required standard.
Never had call back to connections after drilling a drain hole.
 
I would drill a drain hole. Weatherproof fittings make great water tanks. Keeps things cool until it goes bang. A bit of ventilation stops condensation as well.

As to the socket what are you trying to avoid drilling, the socket back or the column?
 
Drilling a drainage hole in high IP rated enclosures, is for condensation purposes, not for compensating for badly sealed glanding. Holes are drilled when these totally sealed enclosures are mounted/located in positions that will be subject to the occurance of condensation forming on the interior of these enclosures. In most circumstances this shouldn't de-rate the enclosure in real terms, as the usually 3.5 or 4mm hole is located at the back edge at the bottom of the enclosure....
 
Where I am if you drill drain hole it will be full of insects in no time. This often causes more problems than water ingress. I would rather use the correct gland for the cable and one of the same IP rating as the enclosure it's going into. You do get glands specifically for flat profile cables. Also only gland underneath the enclosure.
 
Where I am if you drill drain hole it will be full of insects in no time. This often causes more problems than water ingress. I would rather use the correct gland for the cable and one of the same IP rating as the enclosure it's going into. You do get glands specifically for flat profile cables. Also only gland underneath the enclosure.

Hi Marvo
Wee beasties does bother me, though I haven't so far come across a problem with them
Glands for flat cables - where from? Bottom only entry. I agree, but life doesn't always let us - often have 3 cables exiting.

I think Tony and Micknew, above, have hit on the big problem - the accessories don't seal the way that they're meant to - this includes well known makes as well as the more obscure and cheap n cheerful.
Pete
 
It does seem to be a daft thing to do...drill a hole in 'watertight' box. Trouble is (I think) water vapour can sneak in through the tiniest of gaps, condenses inside & then the water can't get out!
 
As pretty much already said, I drill a drain hole to give any water a way out rather than keep it locked in. 3-4MM should keep them bugs out around here.
 
Should add, I used to work a little bit in food factories, and with there chillers keeping the food storage areas cool used to find an office area stuck beside it all the fittings and conduit just filled with water through condensation in no time at all.
 

Reply to Drain holes in Weatherproof Accessories? in the Australia area at ElectriciansForums.net

Similar Threads

Good morning hope everyone is staying safe. I have a question for some of the more experienced sparks, I have a client that wants her outdoor...
Replies
2
Views
4K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock