Discuss DTX readout (split wire) in the Computer and Networking Forum area at ElectriciansForums.net

Reaction score
1
i had dtx done on a 4-wire etherent cable and received a split pair error....; not sure if this definitely means that connector is miswired

also, not sure why is insertion loss so high on pairs 4/5 and 7/8 when it is only a 4-wire setup; dtx is setup for 100base-t...

atached is a pdf of results, if anyone want's to take a look and give their opinion
 

Attachments

  • dtx results.pdf
    259.7 KB · Views: 6
  • dtx results.pdf
    259.7 KB · Views: 2
At first sight, the results show that you have split pairs - basically what should be a pair on pins 1&2 is using one wire each from two different pairs. Ditto for the 3&6 pair. Effectively what it means is that both ends are mis-wired - probably the white/green wire in pin2 and the orange wire in pin3. This is something that the cheap "flashing light" testers will not show you.
The near end crosstalk test (NEXT) shows bad crosstalk between the two pairs according to the graph you have posted but it's not shown in the results table (there should be 6 lines for all the combinations of pairs). The fact that it's not as bad as I'd have expected does lead me to think that perhaps there's some very bad wiring practice been done rather than genuinely split pairs. it may be that someone has (as I've seen done) untwisted loads of wire length - the twists (both within the pairs and between pairs) should be maintained right up to the terminations.
NEXT is a measure of "when you are shouting down one pair, how much of that can you hear in the pair where you should just be hearing the other end" and is possibly more critical than the simple attenuation your test results show.

The TDX graph shows a lot of "mess" in the first (I assume) 100ft of cable. Perhaps this has been badly handled (kinks and the like) which is causing some of the problems. It's not been stapled in place has it ?

TBH, it's a bit confusing to me. NEXT is bad, but not as bad as a genuine split pair problem would produce.

Pairs 4&5, and 7&8 will show massive losses because they aren't connected at all - in principle there should be zero signal reaching the other end, but crosstalk in the connecting leads and test gear at each end will give you a small amount.

But, I'm puzzled by the lack of some figures in the results - e.g. "No Reflection" instead of a length. What length is the cable ? Was the right equipment used at the far end ?
 

Reply to DTX readout (split wire) in the Computer and Networking Forum area at ElectriciansForums.net

Similar Threads

I have unexplained equipment and diagram for three separate connected f81 connectors. Each f81 connector is connected to single receiver to single...
Replies
0
Views
662
My Current Setup (see image BEFORE.jpg): The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit...
Replies
3
Views
3K
So im not terrible as electricasl but also not the greatest. I know how to wire up relays and fuses and all that stuff but the wiring sizes for...
Replies
2
Views
1K
Ok Hello all and thanks for having me. I need some advice and joined this forum hoping to be pointed in the right direction. First off I am not...
Replies
31
Views
4K
Good evening. Finally the futility of the design of my heating system has led me to try and alter it. Central heating is something i'm not...
Replies
24
Views
5K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock