Evening gents bit of advice required please I have recently finished a partial rewire (upstairs sockets upstairs lights and smokes). All is fine apart from when I turned under unit lights on in kitchen it tripped both rcds. There is 1 2 gang switch in kitchen 1 for main kitchen light and 1 for under unit I have taken link out from main light switch the under unit light switch and this rectified the problem no tripping but when I put link back in both tripped again and ideas guys cheers by the way pretty new to the game so be nice
 
You need to carry out an IR test on the suspect circuit, more than likely a NE fault.
 
Big mistake mate with the "new to the game" and "be nice bit"..tripped both RCDs?? christ why does none of this exciting stuff happen to me?
 
As above sounds like crossed neutrals, time to get the tester out
 
Back there tomorrow guys working Sundays love it so will do as advised I have tested all new installation and all is fine gotta test old bit tomorrow looking forward to it a will get back to you with results cheers guys
 
bet it's a shared neutral between 2 lighting circuits or a N in wrong bar in CU.
 
No borrowed neutral all lighting is segregated to individual circuits Everything works fine other than under unit lights
 
Can you do a diagram of how youve wired them? if not I'd have to come round and have a look at £30 per hour......sorry but nothing like this ever happenes to me cos Im perfect.
 
This is exactly the reason why pre-testing is so important and should be as important a job as making sure the kettle is boiled before you kill the power. test test and test again
 
Let us know what the fault is.

I will be nice, all I ask of you is that you do not take offence to any comments! Take it as tea break banter,

and you will be a winner
 
No borrowed neutral all lighting is segregated to individual circuits Everything works fine other than under unit lights

it's possible that the L feed to these under cupboard lights comes from another circuit. rather a borrowed L than a borrowed N.
 
Tenner says its a borrowed neutral , you say that there is a link at the 2 gang kitchen switch , as already mentioned the neutral has got to be from another circuit fed from the other RCD, most likely the kitchen sockets .
 
Tenner says its a borrowed neutral , you say that there is a link at the 2 gang kitchen switch , as already mentioned the neutral has got to be from another circuit fed from the other RCD, most likely the kitchen sockets .
Sounds good to me mate I will check and test tomorrow mate appreciate guys
 
And a pan full of water on the hob..... just in case:)

thinking even further in front / I like it
But make sure you have a lighter or matches in case it is an electric ignitor
 

Reply to Dual rcds tripping in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock