Hi there, I’m just hoping someone could clear something up for me at all. I’m just working my way through some test questions and I’ve come across one in which isn’t making sense to me.

Q. Calculate the maximum earth fault loop impedance permissible for a 30mA RCD used to protect a circuit connected to a TN-S supply.

A. 230/0.03 = 7666ohms (if a TT system, use 50volts, but must use 230volts for a TNS and TNCS system)

Does this all seem correct, or should the question be asking for PFC rather than impedance? If I am misunderstanding, then a short explanation would really put me on the right track with this.

Thanks again in advance for your invaluable help forum.
 
Hi there, I’m just hoping someone could clear something up for me at all. I’m just working my way through some test questions and I’ve come across one in which isn’t making sense to me.

Q. Calculate the maximum earth fault loop impedance permissible for a 30mA RCD used to protect a circuit connected to a TN-S supply.

A. 230/0.03 = 7666ohms (if a TT system, use 50volts, but must use 230volts for a TNS and TNCS system)

Does this all seem correct, or should the question be asking for PFC rather than impedance? If I am misunderstanding, then a short explanation would really put me on the right track with this.

Thanks again in advance for your invaluable help forum.
R=E/I wher R=1667,E=50V, I=0.03. hope this helps.
 
I still don't see the need for them changing it.

I can't see any need for it either, if a circuit has got to 1667ohms there's something seriously wrong, let alone 7667ohms!

Plus people seem to blissfully ignore manufacturers requirements. For example if you look at the instructions for a schneider RCBO it stipulates 100ohms maximum.
 
I can't see any need for it either, if a circuit has got to 1667ohms there's something seriously wrong, let alone 7667ohms!

Plus people seem to blissfully ignore manufacturers requirements. For example if you look at the instructions for a schneider RCBO it stipulates 100ohms maximum.

Been a while since I last used a Schneider RCBO but they also stated that they couldn't be used on TT installations.

I think with the new generation this caveat has been removed.
 

Reply to Earth Fault Loop Impedance... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
596
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi guys was having a conversation as a apprentice I’m still not sure and was wondering why earth fault loop impedance is important if you’ve...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock