Good read all the same. One to file away

Ya they make good docs , only had a flick through and can't say I follow it all, it but when it comes to the A and the B type how will you know whats going on with a basic AC clamp. Leakage current and RCDs is getting so complex

At least with a IR tester you can test all the fixed wiring and basic checks on connected equipment
 
I think if you need to ask other people to justify a purchase you are considering then you will get a mixed response as we all have our own way of getting to the end result of finding the fault. An earth leakage or low current clamp meter is just another tool in the box to aid that hunt for the problem you are presented with and may speed up the fault finding / identification process or it may not
I do have one of the cheaper earth leakage clamp meters it is not something I use everyday / week or month but it was at the right price at the time. With so many potential parallel earth paths in an installation it is worth making sure that the clamp can accommodate the live and neutral tails of an installation as measuring the imbalance of the current will give a more accurate reading than just clamping the earth conductor

In the last few years I have spent more money on logging equipment than anything else as when the fault is an intermittent fault you can guarantee it will never show when you are on site trying to hunt it down and may only show every few days or weeks. My decision has been and was based on many years of fault finding experience and looking at ways of improving how I went about it, it earns it's keep and me money so that is my justification for it's purchase
 
An earth leakage or low current clamp meter is just another tool in the box to aid that hunt for the problem you are presented with and may speed up the fault finding / identification process or it may not
That's what I have been wrestling with. I will likely continue to faultfind successfully without it but any tool that speeds up the process and makes it more convenient is certainly a well worth while investment. I do however feel it would be a little pointless at this stage to buy one that does AC only as I want to future proof
 
That's what I have been wrestling with. I will likely continue to faultfind successfully without it but any tool that speeds up the process and makes it more convenient is certainly a well worth while investment. I do however feel it would be a little pointless at this stage to buy one that does AC only as I want to future proof
I suspect for many years you will fine AC leakage from a lot of electronics is the case to worry about for single/dual RCD bards. At least by measuring it you can explain to the customer why the thing is trip-happy.

I am a little sceptical of DC leaks being a big thing outside of PV and EV, even then many EV charges already have that sort of protection built in.

In the UK / ROI with predominantly TN supplies I expect any fault that exposes AC-derived DC to the metalwork will blow the fuse/MCB anyway, though I can understand in the TT would of much of EU the issue of DC appliance leaks might well be of a deeper growing concern.
 
From my cursory glance through that linked article
What it was saying was the B type let's through 60ma of harmless DC current , whatever that means
Its not blinded by the DC I suppose is the important thing

Now how you go about checking and quantifying all these various leakages and testing is for the "higher ups" than me

Think I'll stick with the Megger and trial and error and multiple RCBOs for problem solving
 
From the article:

"Figure 23 illustrates that Schneider Electric 300mA type A RCDs can be used upstream a 30mA Type B RCD without risk of blinding: Type A protection of the device is guaranteed even in case of a 60mA smooth DC residual current. If the smooth DC residual current reaches the value of 60mA, the 30mA type B RCD will trip"

Seems to be an important point
 
"Figure 23 illustrates that Schneider Electric 300mA type A RCDs can be used upstream a 30mA Type B RCD without risk of blinding: Type A protection of the device is guaranteed even in case of a 60mA smooth DC residual current. If the smooth DC residual current reaches the value of 60mA, the 30mA type B RCD will trip"
See also:
 
20 years ago you could calculate the leakage on a circuit or an installation by running a 250v IR test and doing the math to work out the leakage current. Nowadays with all the standing functional leakage from switchmode power supplies and LED drivers the leakage current rarely bears any resemblence to the IR value measured as a dead test.

I'd say a leakage current clamp meter is an essential item and nowadays and leakage current must be measured as a live test using that device rather than trying to calculate it from an IR dead-test result.

I'm not sure a a clamp meter that measures AC and DC is essential unless you're working with a lot of type-B RCD's.
 
You may want to look at note 2 here in the regs:
531 .3.2 Unwanted tripping
Residual current protective devices shall be selected and erected such as to limit the risk of unwanted tripping. The
following shall be considered:
(i) subdivision ofcircuits with individual associated RCDs. RCDs shall be selected and the circuits subdivided in such a way that any earth leakage current likely to occur during normal operation of the connected load will not cause unwanted tripping of the device. See also Section 314
(ii) in order to avoid unwanted tripping by protective conductor currents and/or earth leakage currents, the accumulation ofsuch currents downstream ofthe RCD shall be not more than 30 % ofthe rated residual operating current
NOTE1: ThiswillalsoallowabetterselectionofthetypeofRCDsaccordingtothenatureofthecircuitortheload.
NOTE 2: RCDs may operate at any value of residual current in excess of50 %of the rated residual current. (iii) use ofshort time-delayed RCDs, provided the applicable requirements ofChapter 41 are met
 

Reply to Earth leakage meter.. Do I really need one? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
477
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
4K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock