Discuss Earth leakage on sockets in the Industrial Electricians' Talk area at ElectriciansForums.net

Sorry, I'm tired. ...Through all socket points tested & also using a voltage pen on the cpc teminal in the ccu

OK, are you measuring 40V between the DB earth bar and the neutral bar?

If so, then there's a high resistance somewhere in the cabling or components between those two bars and the supplier's head where they should be joined (as this is supposed to be TN-C-S).
 
Last edited:
As in the main switch, Neutral tail or main cut out connection?

Yes, if you have a significant voltage between N and E in the board when under load.

Worth checking for volt drop between incoming neutral terminal on main switch and neutral busbar.

I'd be checking tightness of terminals on main switch, link to neutral busbar, and anything else you can get at that isn't sealed up. Careful of any parts that aren't isolated, of course.
 
Hi,so you have a potential,between your probes,a very short distance from where those two points, are one and the same.

If you draw that scenario out,identifying the parts concerned,a clearer view of what may be occurring,will reveal itself :smug:
 
I'm sticking by my previous conclusion.
I'm thinking if the bonding was disconnected you would have 230v between the bars as I don't think you have a neutral.
Turn the main switch off and do a l-n loop test on the incoming side.
That will soon tell you.
Rather than guessing at different voltages.
 
Yes, if you have a significant voltage between N and E in the board when under load.

Worth checking for volt drop between incoming neutral terminal on main switch and neutral busbar.

I'd be checking tightness of terminals on main switch, link to neutral busbar, and anything else you can get at that isn't sealed up. Careful of any parts that aren't isolated, of course.

Cheers for that handysparks. I will investigate that. The whole installation is a bit of a joke so it wouldn't surprise me if it were the case of oversheared tails or untightened terminals (although I did check all the ones on the N bar & RCDs, I didn't check at the main switch).

Cheers again for everyones input. Appreciated
 
I'm sticking by my previous conclusion.
I'm thinking if the bonding was disconnected you would have 230v between the bars as I don't think you have a neutral.
Turn the main switch off and do a l-n loop test on the incoming side.
That will soon tell you.
Rather than guessing at different voltages.

If the supply neutral is lost, how would that give rise to a significant voltage between neutral and earth bars in the DB, given that they're joined at the head?
 
I'm sticking by my previous conclusion.
I'm thinking if the bonding was disconnected you would have 230v between the bars as I don't think you have a neutral.
Turn the main switch off and do a l-n loop test on the incoming side.
That will soon tell you.
Rather than guessing at different voltages.

Sorry rich. just seen this. I will put it on my list to check. cheers
 

Reply to Earth leakage on sockets in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
753
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
608
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock