Hello, im looking for advice on a dorman smith sensel SRD earth leakage relay. I am doing an EICR on a caravan park, the Earthing system is TT and a sensel SRD relay fitted to load side of 200 amp main switch feeding various pillars. Relays have 4 settings from 30mA to 2000mA with time delay also, is this recognised as an RCD as required as I cant achieve RCD trip times from this, maybe faulty, should a 3 phase RCD time delay be installed. Thanks
 
What was the relay set at when you tested it and what test current were you using? What trip times did you get? Did you consult the manufacturers data to know what the tripping times should be for that setting?
What protection is this earth leakage relay providing? Presumably it's fault protection for the TT part of the installation?
 
What was the relay set at when you tested it and what test current were you using? What trip times did you get? Did you consult the manufacturers data to know what the tripping times should be for that setting?
What protection is this earth leakage relay providing? Presumably it's fault protection for the TT part of the installation?

Relay set at 30ma and 0.2 secs, didn't get it to trip on any setting, also test button does not operate main switch, manufacturer gave me trip times info, if this was an RCD I would just fail and replace but I'm nor familiar with this device or how to test it properly.
 
If in doubt read up on what you are dealing with.. then your in a position to make an informed judgement call..

http://www.semitek.cz/tyco/amp_konektory/general/20701_datapak.pdf

About page 35 on the written page number or about 37 if your using your page search.

Check the main switch model and any trip function fitted then read up on that too... took me 30seconds to locate the above info.

Once you have read up on how it all connects and works then your in a good position to answer your own question.

PS never disconnect/open circuit the CT's if the system is powered, never re-energise a system with the CT's open circuit this is very dangerous and can cause very high voltages and fire... if you not sure what I'm talking about then leave any CT connections well alone.
 
Last edited:
Relay set at 30ma and 0.2 secs, didn't get it to trip on any setting, also test button does not operate main switch, manufacturer gave me trip times info, if this was an RCD I would just fail and replace but I'm nor familiar with this device or how to test it properly.

Did you set your tester correctly to account for the 0.2 second tripping delay? Did you hold the test button for long enough to avoid the tripping delay (some earth leakage relays apply the delay to the test button)

If you don't know what you are doing then I would suggest you employ the services of someone who does.
 

Reply to Earth leakage relay in the Auto Electrician Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
860
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm using the stock fuel pump wiring to trigger two different relays for my two fuel pumps on my car built for drag racing. The first relay is a...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock