Discuss Earth loop impedance measurement affected by dimmer switch in the UK Electrical Forum area at ElectriciansForums.net

soms

-
Trainee
Reaction score
49
Working on a job today which included a very simple new lighting circuit.
The lighting circuit a very short run from a distribution board to a single switch position, which then supplies a single luminaire.
The customer wanted a dimmer switch to control the fitting.

To crack on and perform the dead tests, the dimmer was disconnected and the line conductor joined through. The R1+R2 measurement was 0.28 ohms. Polarity checked and insulation resistance measurements taken... all good.

The dimmer was then reconnected and a Zs measurement taken at the end of the circuit.
The dimmer was causing the reading to be >2000 ohms. Is this normal, or acceptable, as it makes you wonder what you happen in the event of a fault on the load side of the dimmer?
With the dimmer bypassed again the reading is fine (approx 26 ohms, on TT system).

So, with my "tin hat on", I guess the following are open to question as well:
Maybe the R1+R2 should have been performed with the switch in place. To speed things up with the insulation resistance testing it was bypassed for all dead testing.
Some say it is dangerous to perform Zs measurements on a light fitting as you have access to live terminals and therefore calculating the value is sufficient and a preferable option.

The light fitting doesn't have any exposed conductive parts and is well out of reach. I didn't actually unpack it and put it up, it is most likely double insulated, one of those self-contained flexible LED strips. It was supplied with a 13A plug which was replaced with a flat 3-pin plug and socket, the socket being the end of our circuit and where the measurements were taken.

I welcome any thoughts.
 
Last edited:
A fault on the load side of the dimmer would invariably trash it causing open circuit, lamps blowing, especially GU10's often have the same result.
Some light fittings can be a pig to carry out a Zs test on, in that case I'd calculate, but would always Zs test if practical.
 

Thank you for the replies, though not so appreciative of being labelled "dumb" but there we go.
Good to hear your opinions on taking Zs measurements.
My knowledge of electronics and in particular dimmer technology is not very good so this was a learning experience for me. The Megger article was helpful in explaining it aswell.
 

Reply to Earth loop impedance measurement affected by dimmer switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
728
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
541
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
281
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
891
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock