I need to fit a 2 way flat plate light switch. When unscrew the old light switch, I can see the Earth cable connected to the metal box that sits in the wall. The Flat plate switch also has a space for an Earth wire.

So, where should the Earth wire go?

Thanks in advance
 
I need to fit a 2 way flat plate light switch. When unscrew the old light switch, I can see the Earth cable connected to the metal box that sits in the wall. The Flat plate switch also has a space for an Earth wire.

So, where should the Earth wire go?

Thanks in advance

dunno.

lol.
 
ideally to both back box and faceplate. the latter being the most important. you either link from back box with a short piece of cable ( sleeved with earth sleeving) or move the connection from back box to faceplate. either way is acceptable, but the faceplate must be earthed.
 

Reply to Earth on flat plate light switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
884
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
447
Hi, I am looking to convert a 2 way light into just control by single switch. I have searched and looked for similar questions here, and found a...
Replies
4
Views
1K
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
719
littletwinn
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock