    Hi chaps,

    Came across this in an EICR today, any thoughts.

    Cheers
    Mark

    IMG_1203.JPG
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    on the left we seem to have a DNO supplied TN-S. on the right some bodge earthing of SWA armour.
     
  3. Mark.W
    Offline

    Mark.W Electrician's Arms

    Location:
    Swindon, Wilts
    Hi telectrix,

    Ok so it's not a PME and TNS then? That's what my first thought was. I thought the right was a separate Neutral
     
  4. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    Would that be one redundant incomer, if so the newer (right side)is a split concentric and TNS - I love the 'cut out caption' questions.

    Edit - the CSA are too large for split concentric
     
    • Agree Agree x 1
  5. Upton Sparks
    Offline

    Upton Sparks Active EF Member

    Location:
    London
    Business Name:
    Kilowatt Electricals Ltd
    Hi Mark .
    Looks good
    what is it ? TN -S or TNC-S ?
    look like there is two cable feeding the service head very odd looking

    If your ZE / ZDB reading are as expected, I would FI it and definitely get the electrical company out to look at it, UKPN or the appropriate company for the area your in.
     
  6. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    looks to me, dno looped in from one house to next doors. you need dno to have look at it. possible tn-s in and pme out.
     
  7. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    TNS in my book looped to next dwelling, then some bodged affair, if that is TNCS , get the DNO out to confirm.
     
    • Agree Agree x 2
    • Bad Spelling Bad Spelling x 1
Loading...
Similar Threads - Earthing arrangement help Forum Date
Strange earthing arrangement. Electrical Forum Mar 16, 2017
Earthing Arrangement? Electrical Forum Jan 30, 2017
Domestic Unsure About An Old Earthing Arrangement Electrical Forum Aug 21, 2016
Earthing arrangement Periodic Inspection Reporting & Certification Jul 20, 2016
Downlight earthing For housing Electrical Forum Tuesday at 11:17 AM
Earthing a gas pipe in attached garage Electrical Forum Aug 11, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job