Discuss Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

I think these overhead earthing systems are being done away with due to copper theives leaving the rural customer without an earth


Not a chance in hell, the cost of taking most of these overhead supplies underground will cost more money than what the banks lost, when the massive fraud scam came to light!! lol!!
 
I was under the impression that we were to assume a value of 16ka(but I could be wrong)
According to the OSG the maximum fault current likely to be found in domestic properties in the UK (unless in heavily built up areas) is 16kA.

However this is probably stated because annex Za of BS60439 provides an additional test, for domestic consumer units that are protected by a BS1361 fuse at the supply, to ensure that a BS60439 consumer unit can take a 16kA fault current without danger.
This permits the use of protective devices in the consumer unit that may not have the short circuit rating to cope with the prospective fault current since the assembly as a whole will cope.
This is part of why the manufactures do not permit different makes of breaker in their consumer units, they say they are not tested for those units.
 
Here's our overhead supply for comparison and comment. Our transformer is served by two high voltage conductors, which in turn come from a string of poles carrying three conductors - ie two of the three branch off to our property. I assumed these were two phases from three phase, but comments here now make me unsure.

IMG_1402-CROP-1280_zps997c4e1c.jpg


One green/yellow sheathed cable comes from the case of the transformer into the ground on the N side of the pole.

IMG_1399-1280_zps7adfd9cd.jpg


On the other side of the pole the two cables out of the transformer join the underground service cable which goes to our meter cabinet. One connects via the isolator or fuse or whatever it is (the grey item), the other is clamped directly. After the join to the service cable, there's another earth that goes underground at the foot of the pole on the S side. The DNO guy who traced and marked the cable routes for us said that this would run some distance horizontally underground while still insulated, then further distance uninsulated.

IMG_1401-CROP-1280_zpsbbbeed37.jpg


Our earthing arrangement was described as "CEW" and also "TN-S" by the DNO engineer, after he opened part of the cut-out to check.

Tony S
 
Last edited:
So does anyone have a picture of a PME system :joker: Seeing as freshman are bound to be seeing that old chestnut.
I know, I know, but the question will be asked, guaranteed.
 
New posts

Reply to Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
524
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock