Hi recently was on a job carrying out EX inspections on three phase motor at a pharmaceutical plant. The supply cable going to the motors does not have a core for the earth they have used the braid/SWA of the cable for earthing. So entering the three phase motor with EXe cable glands terminating the earth Via the gland into a threaded entry into 3 phase motor. Now my question/debate I was having with work colleague was yeah it is entering a threaded entry into enclosure where you will get your earth but the motor terminal box is bolted to the frame of the motor through the 4 fixings bolts, is this adequate to carry the earth through to the motor frame or should it really have banjos then separate earth down to the frame. There is a supplementary earth going from the frame to a local earth boss ? Thanks in advance
 
The earth cable from the earth boss is just going from the structure of the building to the frame of the three phase motor, it’s not directly connected to the earth braiding of the cable just through all the steel structure of the building ? Thats why I’m thinking they should be linked together ?Also it’s braid that has been used, it is suitable for the installation as this is used in many hazardous area locations for more flexibility
 
Is it braided sy or swa? If it's braid then it is not suitable for earthing
Feeding a rotating machine with SWA would not be good practices (Vibration) problems, should be a flexible cable of some sort in my opinion.
 
Yeah that’s what my view is they have earthed the frame with supplementary bond, but the motor terminal box is earthed through the glands and metal to metal flange of the terminal box and the frame are bolted to each other given continuity through to frame from the terminal box. Would this be adequate ?
 
Yeah that’s what my view is they have earthed the frame with supplementary bond, but the motor terminal box is earthed through the glands and metal to metal flange of the terminal box and the frame are bolted to each other given continuity through to frame from the terminal box. Would this be adequate ?
If it’s braid, it’s not reliably earthed.
 
It’s not SY it’s ships wire braid it’s used all the time offshore and in most hazardous area locations. Don’t know the exact Zs as can’t do any live testing and that will be carried out by commissioning, we are just out to do EX inspections but was needing to know regarding the earthing arrangement ?
 
I would if installing this use 4 core ie seperate core for earth. if as you say just inspecting then the minimum i would expect is a seperat earth from supply into motor through seperate gland (Atex stuffer) Not Equipotential bonding.
 
I've seen loads of SY cable used in Ex environments serving motors. Out of interest why isn't compliant and where's this dictated?
The braiding of your bog standard S/Y you could pick up at your local wholesalers is a screen not an earth, it is no to be used as an earth but should be earthed itself (low voltage applications), S/Y is a type of cable design and strictly speaking saying it cannot be used as an earth is incorrect, it comes down to how it has been design and manufactured, there are S/Y's that are suitable for the braiding to act as the earth, however, these are not the S/Y's we can pick up in any wholesaler.

S/Y, C,Y and Y/Y are how a cable construct is arranged and many manufacturers out there have their own specific versions with their own individual design and environmental tolerances.
 
Last edited:
The braiding of your bog standard S/Y you could pick up at your local wholesalers is a screen not an earth, it is no to be used as an earth but should be earthed itself (low voltage applications), S/Y is a type of cable design and strictly speaking saying it cannot be used as an earth is incorrect, it comes down to how it has been design and manufactured, there are S/Y's that are suitable for the braiding to act as the earth, however, these are not the S/Y's we can pick up in any wholesaler.

S/Y, C,Y and Y/Y are how a cable construct is arranged and many manufacturers out there have their own specific versions with their own individual design and environmental tolerances.
Accepted Darkwood, that wasn’t my question. Where I’ve seen it installed the CPC has always been a separate dedicated core. My query was regarding Robs statement that it wasn’t compliant in a Ex environment. I just simply wanted clarification of this and where/what regs precluded it’s use.
 
Accepted Darkwood, that wasn’t my question. Where I’ve seen it installed the CPC has always been a separate dedicated core. My query was regarding Robs statement that it wasn’t compliant in a Ex environment. I just simply wanted clarification of this and where/what regs precluded it’s use.


It's product standards and cable glands do not meet what is required to be used as an exd cable. Could be used in Exe situations, but as you know a 3ph motor cant comply with this type of design.
 
Standard practice in hazardous areas is 3 core swa or braided bfou cabling with the motor frame tied to local earth at the skid earth boss. Perfectly acceptable, and Zs values for fuses are checked during initial inspections.
It can be hard to calculate expected continuity readings when parallel earths are used this way!

The braid or swa is obviously tied down at the mcc side in the switch room etc.
 

Reply to Earthing of Three phase Motor in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
Hi, I am trying to wire a two speed switch to a three phase motor. I have continuity checked the switch in both positions 1 - Low and 2 -High (See...
Replies
1
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I’ve recently seen a motor wired directly from the local isolator to the motor terminal box in 3 core 1.5mm cable. The gland has been made off...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock