Hi everyone, just learning a bit more about writing up EICRs. I have a situation where I have a 3 phase board with a sub main going to a small office which has a consumer unit in it. The sub main board is supplied by and MCb in the 3 phase board obviously making it into a single phase board in the small office.

The office has a 3 way board with a main switch and rcbos, this is ther board I need to test. With the paperwork in a little confused, would this go on a IPN18C as is a three phase supply, then putting the main ze and pfc of the 3 phase board in part 8 (supply) and then put then put the details of the MCb feeding small CCu in part 9?

Any help advice would be greatly appreciated.
 
The supply is the supply. Always. No matter what.
So test the supply at the origin and record results.

Then test the office board you exactly as you would a domestic install.

There will be a section that says "Only complete where the board is not connected to the origin" (or similar depending on the exact form layout). There you record where the OCPD is for the distribution circuit is, what type of OCPD it is, and record the Zs and PFC for the distribution circuit. If the distribution circuit is RCD protected record the RCD results for it too.

Job done.
 
The supply is the supply. Always. No matter what.
So test the supply at the origin and record results.

Then test the office board you exactly as you would a domestic install.

There will be a section that says "Only complete where the board is not connected to the origin" (or similar depending on the exact form layout). There you record where the OCPD is for the distribution circuit is, what type of OCPD it is, and record the Zs and PFC for the distribution circuit. If the distribution circuit is RCD protected record the RCD results for it too.

Job done.
Thanks for your response, yeah Ive found the bit you mean, TO BE COMPLETED ONLY IF THE DB IS NOT CONNECTED DIRECTLY TO THE ORIGIN OF THE INSTALLATION- under this bit it is asking for nominal voltage and number of phases, would that be in regards to the single phase supply to secondary board or the original 3 phase board?
 

Reply to EICR advice needed!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
925
Afternoon! Hoping someone has experience working on the ABB gear below. It’s in a Mobile Office/ Welfare unit, supplied via either 230v hook up...
Replies
0
Views
251
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock