Seeing as i started the debate i would like to close it by saying that i have to agree wholeheartedly with Chris, badged01 and biff on the subject. I'm not saying or suggesting that what Geoff or DSkelton offer up is wrong merely that there interpretation seems to miss the point that section 7 of BS7671 asks for SB to be applied if the 3 conditions are not met. The points put forward by badged01 define very clearly what section 7 asks for. Regardless of any satisfactory results gained during tests proving that the resistance is low enough, the crux of the matter is that SB is REQUIRED in a room containing a bath or shower.
 
Last edited by a moderator:
Im happy to accept the views of anybody if this damn thread is closed and put to bed ...... its turned out to be like opening a whole can of worms!
 
Nooooooooooooooooooooooooooooooo. You cannot end it on such a flawed statement.

Geoff or DSkelton is wrong merely that there interpretation seems to miss the point that section 7 of BS7671 asks for SB to be applied if the 3 conditions are not met.
You must apply 415.2 unless the three conditions are met.

This is not an interpretation; that is what it says.



All RCBOs are RCDs but not all RCDs are RCBOs.
 
Nooooooooooooooooooooooooooooooo. You cannot end it on such a flawed statement.


You must apply 415.2 unless the three conditions are met.

This is not an interpretation; that is what it says.



All RCBOs are RCDs but not all RCDs are RCBOs.

Geoff you are clearly very opinionated. Its pretty simple, 701 require SB to 415.2, it then modifys and supplements it with further requirement's.

1) it asks for Local, this isn't mentioned in 415.2, its supplementary.

2)it asks for the SB to be connected to the terminals of the protective conductors of equipment in the location and to be connected to extraneous parts either in the location or at entry.

Its pretty explicit and clear.

Now your touch voltage concept id flawed, it obeys ohms law, end of, there no debate to be had.

The original IEC uses Ut= If(max fault current) x Rbw(resistance of cable), its been adjusted to 50/Ia by BS7671 based on certain assumptions. Now using your method Ut(touch voltage) will be a product of (If), it may result in Ut be greater than 100 volts, even 150 volts

Now install a SB and we have a Current divider, assume little current flow in the SB in relation to R2 and we have a very low Ut(touch voltage).

Little knowledge can be dangerous, don't play with touch voltages unless you fully understand them, and to advise people SB is not required, well what can i say.

Chris
 
Last edited:
New posts

Reply to EICR and Supplementary Bonding. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock