Discuss EICR code for the below picture in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

A bit more context is needed here.

The use of "choc blocks" is OK in an enclosure, but it appears this might not be enclosed. Also it looks like the body of the lamp is metallic (but painted black), however, there appears to be no CPC (earth wire) connected to that.
 
That looks like rubber insulation to me but not very clear.
Is this an EICR or an exam question.
 
As far as I am concerned that is a C2 (potential danger) as their is no earth (cpc) on what appears a metal lamp base
 
What markings are on the lamp? Double insulated symbol (two concentric squares)? Suitable for a flammable surface (F in a triangle)?
What condition is the rubber (?) insulation of the wires in? Is there a cpc present?
 
What markings are on the lamp? Double insulated symbol (two concentric squares)? Suitable for a flammable surface (F in a triangle)?
What condition is the rubber (?) insulation of the wires in? Is there a cpc present?
I think the equipment shown predates the concentric squares symbol by several decades.

C1 for exposed connections in its current state.

Equipment is disassembled, and there’s no cpc. That’s two faults. I would say immediately dangerous.

However, you could be pedantic and say, if it’s not part of an energised system, then should it be coded at all?? There’s no information about that, only an assumption.
 

Reply to EICR code for the below picture in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
572
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
531
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
403
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock