Discuss Eicr code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

sparky87

hi all, done a eicr recently and found the following and would like thoughts on the codes? Thinking code 2 but bit harsh to fail the installation on these points esp as its been like it for 30 ish years and no problems or atleast that's what the owner will say!!

Cpc used as live on landing 2way switch ( both points have a cpc connected.

Single insulated cables buried in the walk and voids.

Black single insulated cable used as cpc for kitchen light point

In advice would be great.

Cheers
 
It's hardly harsh to point out that those are all potentially dangerous defects! It would be criminally insane to suggest that the installation is suitable to be in service in that condition regardless of how long it has been like that.
 
Ahh now then, I assume the box did not have a plate on it?

So, that's a 47mm box, buried probably another 20mm from finished plaster level.

On that basis, the cable itself is more than 50mm from the surface, so no code.

The termination of the cable is a pile of poo, and should at least be in a Wago, so probably only deserves a C3.

I'll get me coat.
 
Found this on a 10 year old block of apartments, the 5th apartment I went in, a 5x5mm hole in the wall drew my attention.. then the lack of shaver point like the others had made me tap away at the hole, until this was found!
 
You didn't have to cut it in or chase in the 47mm and you had one in your stock - every sparks dream of a good day, result I say!
 
The CPC on the two way lighting is in T&E I presume....Could be in flex, though very unlikely. To the OP, you are there to report not to make friends. The ESF guide is pretty decent for example codes. But you should know that using an uninsulated CPC as a live conductor is not good...not good at all.
 
As a QS you are supposed to be telling other less informed Electricians if and where they are going wrong, the questions you ask should not becoming from yourself, you should know what is right or wrong.
 

Reply to Eicr code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
804
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
786
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock