Discuss EICR codes .... AGAIN! in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

I was called today and asked for my opinion on a report a Landlord has had done. The property is about 17 years old.

These are the 4 items highlighted on the report:

1. 4.4 CU does not comply with amendment 3 fire rating regulations - C3

2. 4.9 Circuits are unidentified at CU - C2

3. 5.11.3 Circuits with cables buried in walls are non RCD protected in various locations - C2

4. 8.1.1 Circuit serving bathroom is non RCD protected - C2

Interestingly the comments says:

The installation has been superceded by the 17th Edition Wiring regs

On the schedule of circuit test results the there is no end to end continuity on the CPC of one of the socket circuits.... not mentioned in the "findings" -

So my codes:

1. C3

2. Comment only

3. C3

4. C3

and for the CPC being non continuous - C2

Oh and the quote for remedial action is change CU to AMD 3 unit and investigate the lack of continuity of the CPC on the socket circuit. Fixed price of £350 + VAT


Thoughts

PS :

This is a NICEIC registered sparky and this is lifted directly from their website:

"When you need electrical work carrying out you may want to choose NICEIC registered contractors because this will ensure the level of service you receive is guaranteed. When electricians are registered it means they are monitored and have to abide by the strict guidelines and regulations When applying to join the scheme a contractor must go through an assessment to make sure their level of work is up to the standards of the scheme."

Hum.......
 
I would C3 the bathroom for no rcd protection
However if there is no supplementary equipotential bonding in place to extraneous metal work in the location then That would make that item inspected a C2.
The unidentifiable circuits , if I thought they may give rise to danger then I would put FI.
If you mean circuits not labelled I would actually C3 it same goes for lack of circuit charts/labels etc.
 
Last edited:
I was called today and asked for my opinion on a report a Landlord has had done. The property is about 17 years old.

These are the 4 items highlighted on the report:

1. 4.4 CU does not comply with amendment 3 fire rating regulations - C3

2. 4.9 Circuits are unidentified at CU - C2

3. 5.11.3 Circuits with cables buried in walls are non RCD protected in various locations - C2

4. 8.1.1 Circuit serving bathroom is non RCD protected - C2

Interestingly the comments says:

The installation has been superceded by the 17th Edition Wiring regs

On the schedule of circuit test results the there is no end to end continuity on the CPC of one of the socket circuits.... not mentioned in the "findings" -

So my codes:

1. C3

2. Comment only

3. C3

4. C3

and for the CPC being non continuous - C2

Oh and the quote for remedial action is change CU to AMD 3 unit and investigate the lack of continuity of the CPC on the socket circuit. Fixed price of £350 + VAT


Thoughts

PS :

This is a NICEIC registered sparky and this is lifted directly from their website:

"When you need electrical work carrying out you may want to choose NICEIC registered contractors because this will ensure the level of service you receive is guaranteed. When electricians are registered it means they are monitored and have to abide by the strict guidelines and regulations When applying to join the scheme a contractor must go through an assessment to make sure their level of work is up to the standards of the scheme."

Hum.......
Humm I agree
 

Reply to EICR codes .... AGAIN! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
645
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
415
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock