Discuss Eicr details in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

juanpabs

Hi all just a little query about a conversation I was having with a work mate.

Personally I do a few domestic EICR's on occasion and whom I was talking to does more large commercial and industrial. Now when I perform my inspections I would usually start with a 20% sample and depending on these results would complete the forms or do more testing if I had unsatisfactory results. On these small installations without opening up all points I can still perform all tests on each circuit seeing as there are only say 6 to 10 in a house or flat. End result is my schedule of test results looks totally filled out with readings for R1+R2, end to end, Zs ect. Yet this got me thinking to how I would fill out a schedule of test results on a larger install say with 10 lighting circuits with the same 20% starting point, would I just pick out 2 circuits, test them as I would usually to ensure compliance, fill these results into the schedule and here comes my question! Would I just put in the details of the other circuits but leave out any column that would usually have a test result in them? This would just strike me as strange to look at if I seen a certificate with values missing!

Cheers for any replies to what might be a quite a silly question.
 
For any one circuit you assess everything that is visible and accessible and also internally inspect, say, 20% of accessories and joints, increasing this number if results are bad. You also take note of the circuit details.
On that circuit you test continuity of earthing, IR, and polarity. this is a 100% test of the circuit.

If you have a house then this would be repeated for each circuit.

If you are doing a commercial or industrial EICR there could be significant limitations on what you can do and a 100% testing may not be possible, therefore you stage the arrangements so that 100% testing of, say, 30% of the circuits is done this year and so on, remembering to change the circuits tested each year!
External inspections of the entire installation and 20% internal inspection of the circuits tested can be undertaken, circuit details can still be entered and the extent and limitations indicates the reasoning behind what you have done.
 
If I am signing a cert then personally I test everything, with the exception of not pulling up floor boards I treat it as a new job, with just taking a odd socket/switch off to check if sleeving is fitted etc

I have heard of sparks entering a front door and they have gone within half-hour after testing a 3 bed room house, now that's not testing that's just making money isn't it lol
 

Reply to Eicr details in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
613
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
840
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock