Discuss EICR - Help on my Request for Electrical Safety Alternatives and Quotes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Good morning,

We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues categorised as C1, C2, and C3 were identified.

I've tries to discuss alternatives with the engineer, particularly concerning the replacement of the consumer unit (CU) due to its high cost. However, I'm not satisfied with the options provided. Could you please share your thoughts on achieving safety compliance without replacing the CU, and costing a small fortune?

On the loose box above the CU issue, it has a bit of play, minor, it is not hanging of the wall!

Quotes asked:
  1. Engineer to provide a quote for removing the door contactor switch to address the C1 issue?
  2. What would be the cost for securing the loose box above the CU?
Here are my specific questions:
  1. Could the engineer quote for replacing the three B16 MCBs with B10s?
  2. Is it possible for the engineer to group the two ring circuits and isolate the radial circuit, or group it with a B20 circuit? Please provide a quote for this work.
  3. Will the proposed solutions from points 1 to 4 ensure compliance and enable the issuance of an EICR?

Ultimately, I'm looking to resolve these issues without needing to replace the CU. I appreciate your guidance on this matter.
Please see the PDF as it includes pictures.

Thank you for your assistance.

Lucio


2024-04-24_07-58-57.jpg
 

Attachments

  • QUOTE - 33224 - EICR (Electrical Installation Condition Report).pdf
    1.6 MB · Views: 35
They failed to note you have type AC RCDs which are now generally deemed unsuitable and the RCD test notice no longer complies.
 
That EICR lacks a lot of detail and bears little or no resemblance to the model forms in BS7671
Where are the Installation details, circuit test results and all the other information that a proper EICR details
Looks like the contractor is big on the gloss but lacks the substance
 
Hi All;

Thank you for your comments, attached is the full report. I had taken a picture of the actual report for brevity.

Many thanks

Lucio
There are some valid issues . But the whole EICR "game" is open to so much abuse as they can almost do what they want and many do as they want to make money from the work required . It seems many people doing them have varied interpretations of the regs etc .
 
No 2 although maybe accurate if cables clipped direct 16 amp would be ok, obviously 1.5 is better suited to 10 amp but you could not say for definate a 16 amp MCB is too big for a 1.5mm2 cable, lots of reasons why it may be compliant
 
Item 4 is questionable. If the radial only serves a single point it is fine but if multiple points it needs addressing.
It isn't questionable at all, it's just wrong - what reg prohibits a radial and ring sharing an MCB ?
More likely the combination of radial cable size and MCB rating isn't acceptable - e.g. multiple sockets, 2.5mm T&E, B32 MCB. if the MCB were 20A or 25A then it would be fine. If it were 4mm cable it would be fine.
 
It isn't questionable at all, it's just wrong - what reg prohibits a radial and ring sharing an MCB ?
More likely the combination of radial cable size and MCB rating isn't acceptable - e.g. multiple sockets, 2.5mm T&E, B32 MCB. if the MCB were 20A or 25A then it would be fine. If it were 4mm cable it would be fine.
As I said it is questionable and my query was perfectly correct. For you to suggest a 2.5 on a 25A protective device is fine without knowing the installation method is, well, questionable. Not sure how the 32A protective device being type B is relevant.
 
It isn't questionable at all, it's just wrong - what reg prohibits a radial and ring sharing an MCB ?
More likely the combination of radial cable size and MCB rating isn't acceptable - e.g. multiple sockets, 2.5mm T&E, B32 MCB. if the MCB were 20A or 25A then it would be fine. If it were 4mm cable it would be fine.

But if that extra cable only feeds one point then it is not a radial circuit but is a completely compliant spur from the ring.
So yes, it is questionable.
 
But if that extra cable only feeds one point then it is not a radial circuit but is a completely compliant spur from the ring.
So yes, it is questionable.
A radial circuit in its own right emanates from a consumer unit or power source, where as a spur is a branch off of an existing circuit
 
But a spur on a ring can be taken from any point on the ring, including at the MCB.
Then in my opinion it's not a spur.
If it was taken from a point on the ring then it would be a spur.

Would disconnecting the ring from the mcb then make it a radial ?
 
Then in my opinion it's not a spur.
If it was taken from a point on the ring then it would be a spur.

Would disconnecting the ring from the mcb then make it a radial ?

It is just a part of the ring though - a spur as per the regs.

Yes if you removed the whole ring then it would become a radial with one point.
 

Reply to EICR - Help on my Request for Electrical Safety Alternatives and Quotes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I know I’m very health and safety conscious and electrical safety has always got me thinking with various sparks saying different things in...
Replies
27
Views
3K
Hi, hopefully, you can help me by giving some guidance over the EICR which has failed for my rented property. It was carried out by an electrician...
Replies
16
Views
4K
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
10K
I wonder if any electricians can offer some advice? I feel that I may be getting taken for a ride. I rent out a 2 bedroom flat built in 2005 that...
Replies
53
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock