Search the forum,

Discuss EICR Limitation - no L to N IR Test in the UK Electrical Forum area at ElectriciansForums.net

Seriously? You don't even know the alternative Zs test method?

With the circuit isolated at the mcb:
Link L to E at the far end of the circuit
Connect the tester live probe to the incoming L of the RCD
Connect the tester E probe to the outgoing side of the appropriate MCB
Carry out the test.

This way you are testing exactly the same circuit but from a different point within the circuit.
I didn't know that either. Another nugget of knowledge I've learned today!
 
There is no reason why this test should be omitted ,especially in a house,where I would of thought it would be no problem isolating all equipment plugged in etc,cheers
A little more difficult in a warehouse though, the roof is 5 or 6 metres from floor level and they don't want to shift things around so you can get access to delamp. For example.
 
Thanks for all your replys, In my opinion I think it's a bit lazy not to check in this circunstance but I presume he said to the client it will be an extra £££ to do this and they said well don't bother but I can fully understand in some circumstances and definitely in commercial jobs.
 
Was the IR tested by linking the L+N and testing to earth?
I don't have the latest copy of GN3, but I would be very concerned that it would suggest the results of a test can be calculated.
I would also wonder what point would be served by recording such a value?
 
Could you please explain how to do a live Zs test 'correctly' when there is an RCD present?

.

Seriously? You don't even know the alternative Zs test method?

With the circuit isolated at the mcb:
Link L to E at the far end of the circuit
Connect the tester live probe to the incoming L of the RCD
Connect the tester E probe to the outgoing side of the appropriate MCB
Carry out the test.

This way you are testing exactly the same circuit but from a different point within the circuit.

Brilliant tip!!! Thanks
 

Reply to EICR Limitation - no L to N IR Test in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock