Discuss EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
29
Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon. No reported problems.

I expected to be in and out in about 3-4 hours to be honest, and as expected I found nothing wrong until I began my ring final tests. All the sockets had already tested fine during my visual check and quick test with my Kewtech tester. I was a little surprised to find this property only had the one ring with the combi boiler also hanging off it, given the board was a 10-way with 4 spare ways in it. Made me wonder why during the rewire the property wasn't split into an upstairs and downstairs ring, but anyway....

So, RN tested out fine, but R1 - open circuit, R2 - open circuit ! Oh joy. At this point the current tenant piped up and said "Should I have mentioned some of the sockets were getting hot ?!"

Anyway according to the Codebreakers guide I should be giving this a C2 (Actually I'm thinking of giving it an FI), and handing the report to the landlord. I admit I don't get many outright failures, but this one obviously is.

Anyway what I was going to ask is I'm assuming what I have here is a ring that's functioning as 2 overloaded radials, and somewhere both conductors have a break in them (It'll be just my luck that they will be in different locations). It can't be classed a C1 can it, as this fault could have been there for years, and another couple of days shouldn't hurt. What would you classify this as - C1, C2 or an FI ?
 
Last edited:
An open circuit on any conductor on a ring final circuit should attract a C2. What limitations are preventing you inspecting and testing thus giving an FI code?
The FI code is massively misunderstood and misused, it should be used when a limitation in the inspection prevents you from assessing something and where did to the limitations, you suspect danger or potential danger.
 
C2 for me,

Also, odds are that the cable faults are in exactly the same position.

could be a classic diy mistake, drill hole for picture hook. bang goes electric off.
"turned power back on to see if everything was ok"
found all lights and sockets still working, therefore everything is ok!!!
unseen is the hole blown in live and cpc hidden out of sight.

p.s. replace hole for picture hook with any of the following
nail for picture, floorboard, etc.

screw for floorboard, doorframe, shelf, tv bracket, doorbell, coat hooks, etc.
 
I disagree @Paignton pete and @buzzlightyear

This is an inspection only.

there is no further investigation required, a fault has been found in 2 conductors of a ring.
report it's condition as C2 and move on.

if it was not a ring, and the cpc was broken, It may well be a C1, no further investigation is required to find where it is broken. just report it and move on.

Obviously to fix the fault will require further investigation (AKA Fault Finding) as it has not been precisely located.
 
Code FI (Further investigation required without delay)
It should usually be possible for the inspector to attribute a Classification code to each observation without indicating a need for further investigation.
However, where ‘FI’ has been entered against an observation the inspector considers that further investigation of that observation is likely to reveal danger or potential danger that, due to the agreed extent or limitations of the inspection and/or testing, could not be fully identified at the time.

I don’t see how this is relevant to an open circuit on a ring final there’s an open circuit that’s been identified, especially when the regulations require that each conductor is to be continuous.
 

Reply to EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
947
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
761
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock