Discuss EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

oh don't worry about offending me, i am open to discussion, not laying down the law!

my way of looking at it would be that there is a high risk of overloading a conductor because the ring is broken and the ocpd is higher than the current capacity of the cable.
couple of heaters plugged in on a cold night and the cable could be seriously overheated and no trip of breaker to protect it.

rcd wont help until the cable has melted beyond holding the conductors apart.
 
That make zero sense, it’s potentially dangerous if the continuity is high but it’s not potentially dangerous if it’s open circuit which is worse?

sorry , what I ment was I would be happy to convert into a pair of long radials if I could achieve the relevant readings for a 16/20a radial and downgrade the mcb

if it has to remain a rfc then I would FI it and insist the missing link / missing connection be found
 
So, RN tested out fine, but R1 - open circuit, R2 - open circuit ! Oh joy. At this point the current tenant piped up and said "Should I have mentioned some of the sockets were getting hot ?!"

Anyway according to the Codebreakers guide I should be giving this a C2 (Actually I'm thinking of giving it an FI), and handing the report to the landlord. I admit I don't get many outright failures, but this one obviously is.

In this case, i see no reason to stray from the codebreakers advice.

also as mentioned, some sockets getting hot, leads me to think there is a very high chance of some overloaded cables or terminals.

It is potentially dangerous.
do you need to do further investigation to figure out if it is dangerous?
as a temporary fix, improvement the ocpd could be changed for a 20A (still leaving the possibility of some free cable ends floating around somewhere)
but really it needs marking down as a failure so it gets repaired.
 
As a temporary fix reducing the OCPD size will work however the broken conductor needs to be found. This needs to be repaired as a lose conductor could potentially be fatal.
 
As a temporary fix reducing the OCPD size will work however the broken conductor needs to be found. This needs to be repaired as a lose conductor could potentially be fatal.
You are Quite correct, I did fail to make that clear in my post.
Well spotted.
 
I think the confusion comes from the fact to rectify a brocken ring requires investigation and further testing. But this is an EICR and you are reporting on the condition of the installation. So in this case a brocken ring has been identified. Which will become dangerous if the circuit is overloaded . No further investigation is required to find out if the brocken ring is potentially dangerous .we know it is . So I would code 2 it
 

Reply to EICR - No Line or CPC Continuity on Ring in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
959
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
761
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
910

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock